Owner -project manager - Electrician Talk - Professional Electrical Contractors Forum
CLICK HERE AND JOIN OUR COMMUNITY TODAY, IT'S FREE!
Go Back   Electrician Talk - Professional Electrical Contractors Forum > Electrical Trade Topics > NEC Code Forum
Like Tree1Likes
  • 1 Post By FaultCurrent
Thread Tools Display Modes
Old 03-12-2019, 08:58 PM   #1
Default Owner -project manager
So a question for those who do high rises.
I am beginning to run a job in a high rise hotel. The top floor sits 78’ off the ground level. I been doing some research and think that both NEC and IBC codes require 2hour fire rated wiring for elevators, and all emergencies circuits required for fire related situation. Meaning all elevator related, smoke removal fans, stairway pressurization, and the power circuits to the fire command center. Maybe others, but I think this covers the ones in this job.
IBC 27, and 30, NEC 700.10 .
The fire alarm is a “one up one down” system (as it was called to me) and has a mass evac system. It’s an 8 story hotel.
So I’m being told by the job super and my higher ups that I’m over thinking it and none of it applies. Am I? Or am I correct? I just want to try to prevent the nightmare later of haveing to come up with solutions to thhn inside emt for everything. By the way the fire pump will be ran underground under slab to address that 2 hour rating.
Any advice or input would be greatly appreciated.
Thanks
68Camaro is offline   Reply With Quote
Sponsored Links
Advertisement
Old 03-13-2019, 12:39 PM   #2
FaultCurrent's Avatar
Rewards Points: 927
You are over thinking it. Since the building is fully sprinklered (I assume) you are not required to have the 2 hr protection for the circuits you mentioned. The floor above and floor below voice evac is determined by the Fire Marshal and Fire Alarm Installer. Local jurisdiction call. Regardless, all those details should be supplied in the engineered plans.
No need to try and engineer it yourself. Submit an RFI if you feel strongly something is wrong and be prepared to back it up.
splatz likes this.
At it since 1971 and still going....kind of.
To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts.
Grandpa was old, and he was slow. But he got there.
FaultCurrent is offline   Reply With Quote
The Following User Says Thank You to FaultCurrent For This Useful Post:
Southeast Power (03-18-2019)
Old 03-13-2019, 04:38 PM   #3
Old Grumpy Bastard
MechanicalDVR's Avatar
Rewards Points: 2,874
+1 for Fault's answer.
High rise = all systems professionally engineered, signed and sealed.
Warning:
I've been known to make snowflakes whine!
Posts may contain sarcasm and guttural humor!
MechanicalDVR is offline   Reply With Quote
Sponsored Links
Advertisement
Old 03-13-2019, 06:54 PM   #4
Ok thanks for replies. The plans call out for elevator wiring to be 2 hr rated. Did not for the other items, so my concern was it was assumed we should. When I asked one or two others, the answer was no. But never said why. Like because of the sprinklers. And yes it’s fully sprinklered. I am glad to be wrong on those issues.
By the way, the plans call for the fire alarm to be “all devices back to the FACPin 3/4 conduit, no plenum cable” it’s a class A system. Those words are spelled out on drawings. Would that mean no MC or would Mc cable be equivalent? Yes it can’t be free aired wire, but would MC be ok?
Thanks for the responses
Old 03-18-2019, 09:56 PM   #5
DashDingo's Avatar
Rewards Points: 22
Originally Posted by 68Camaro View Post
Ok thanks for replies. The plans call out for elevator wiring to be 2 hr rated. Did not for the other items, so my concern was it was assumed we should. When I asked one or two others, the answer was no. But never said why. Like because of the sprinklers. And yes itís fully sprinklered. I am glad to be wrong on those issues.
By the way, the plans call for the fire alarm to be ďall devices back to the FACPin 3/4 conduit, no plenum cableĒ itís a class A system. Those words are spelled out on drawings. Would that mean no MC or would Mc cable be equivalent? Yes it canít be free aired wire, but would MC be ok?
Are you talking wiring method in the shaft?
Sent from my iPhone using Tapatalk
DashDingo is online now   Reply With Quote
Old 03-18-2019, 10:12 PM   #6
Southeast Power's Avatar
Rewards Points: 8,634
You have to look in the specs and the shop drawings for the fire alarm system.
The plans are nice but the specifications supersede the plans.
It is going to come down to what the owner paid for and if what they paid for conforms to whatever fire ordinances the local Fire Marshal decides.
Southeast Power is online now   Reply With Quote
Thread Tools
Owner and project manager 68Camaro New Member Introductions 9 03-15-2019 12:24 AM
Erick Martinez - Project Manager ace1807 New Member Introductions 4 03-21-2018 02:37 PM
Hiring Project Manager/Electrical Estimator Everette WA Robin.v Looking To Hire 0 01-06-2017 02:11 PM
Project Manager pay expectation All4uonline General Electrical Discussion 3 11-28-2016 01:08 AM
Southern Cali- Ontario Project Niguel Electric Looking To Hire 0 01-14-2016 11:19 PM
Powered by vBulletin® Version 3.8.8
Copyright ©2000 - 2020, vBulletin Solutions, Inc.
Search Engine Optimization by vBSEO 3.6.1
vBulletin Security provided by vBSecurity v2.2.2 (Pro) - vBulletin Mods & Addons Copyright © 2020 DragonByte Technologies Ltd.
User Alert System provided by Advanced User Tagging (Pro) - vBulletin Mods & Addons Copyright © 2020 DragonByte Technologies Ltd.
Our Pro Sites Network
ContractorTalk.com | DrywallTalk.com | HVACSite.com | PaintTalk.com | PlumbingZone.com | RoofingTalk.com