Old 03-12-2019, 08:58 PM   #1
Junior Member
 
Join Date: Mar 2019
Posts: 4
Default Owner -project manager

So a question for those who do high rises.
I am beginning to run a job in a high rise hotel. The top floor sits 78’ off the ground level. I been doing some research and think that both NEC and IBC codes require 2hour fire rated wiring for elevators, and all emergencies circuits required for fire related situation. Meaning all elevator related, smoke removal fans, stairway pressurization, and the power circuits to the fire command center. Maybe others, but I think this covers the ones in this job.
IBC 27, and 30, NEC 700.10 .
The fire alarm is a “one up one down” system (as it was called to me) and has a mass evac system. It’s an 8 story hotel.
So I’m being told by the job super and my higher ups that I’m over thinking it and none of it applies. Am I? Or am I correct? I just want to try to prevent the nightmare later of haveing to come up with solutions to thhn inside emt for everything. By the way the fire pump will be ran underground under slab to address that 2 hour rating.
Any advice or input would be greatly appreciated.
Thanks
68Camaro is offline   Reply With Quote
Join Contractor Talk

Join the #1 Electrician Forum Today - It's Totally Free!

ElectricianTalk.com - Are you a Professional Electrical Contractor? If so we invite you to join our community and see what it has to offer. Our site is specifically designed for you and it's the leading place for electricians to meet online. No homeowners asking DIY questions. Just fellow tradesmen who enjoy talking about their business, their trade, and anything else that comes up. No matter what your specialty is you'll find that ElectricianTalk.com is a great community to join. Best of all it's totally free!

Join ElectricianTalk.com - Click Here JOIN FOR FREE


Warning: The topics covered on this site include activities in which there exists the potential for serious injury or death. ElectricianTalk.com DOES NOT guarantee the accuracy or completeness of any information contained on this site. Always use proper safety precaution and reference reliable outside sources before attempting any construction or remodeling task!

Sponsored Links
Advertisement
 
Old 03-13-2019, 12:39 PM   #2
Senior Member
 
FaultCurrent's Avatar
 
Join Date: May 2014
Location: California
Posts: 490
Rewards Points: 919
Default

You are over thinking it. Since the building is fully sprinklered (I assume) you are not required to have the 2 hr protection for the circuits you mentioned. The floor above and floor below voice evac is determined by the Fire Marshal and Fire Alarm Installer. Local jurisdiction call. Regardless, all those details should be supplied in the engineered plans.
No need to try and engineer it yourself. Submit an RFI if you feel strongly something is wrong and be prepared to back it up.
splatz likes this.
__________________
At it since 1971 and still going....kind of.
To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts.

Grandpa was old, and he was slow. But he got there.
FaultCurrent is offline   Reply With Quote
The Following User Says Thank You to FaultCurrent For This Useful Post:
Southeast Power (03-18-2019)
Old 03-13-2019, 04:38 PM   #3
Old Grumpy Bastard
 
MechanicalDVR's Avatar
 
Join Date: Dec 2007
Location: "Old Dominion"
Posts: 59,888
Rewards Points: 2,188
Default

+1 for Fault's answer.

High rise = all systems professionally engineered, signed and sealed.
__________________
I'm as Christian as possible in the times we live in.

Always just a stallion in a china shop
MechanicalDVR is online now   Reply With Quote
Sponsored Links
Advertisement
 
Old 03-13-2019, 06:54 PM   #4
Junior Member
 
Join Date: Mar 2019
Posts: 4
Default

Ok thanks for replies. The plans call out for elevator wiring to be 2 hr rated. Did not for the other items, so my concern was it was assumed we should. When I asked one or two others, the answer was no. But never said why. Like because of the sprinklers. And yes it’s fully sprinklered. I am glad to be wrong on those issues.

By the way, the plans call for the fire alarm to be “all devices back to the FACPin 3/4 conduit, no plenum cable” it’s a class A system. Those words are spelled out on drawings. Would that mean no MC or would Mc cable be equivalent? Yes it can’t be free aired wire, but would MC be ok?

Thanks for the responses
68Camaro is offline   Reply With Quote
Old 03-18-2019, 09:56 PM   #5
Senior Member
 
DashDingo's Avatar
 
Join Date: Feb 2018
Location: Minnesota
Posts: 130
Rewards Points: 20
Default

Quote:
Originally Posted by 68Camaro View Post
Ok thanks for replies. The plans call out for elevator wiring to be 2 hr rated. Did not for the other items, so my concern was it was assumed we should. When I asked one or two others, the answer was no. But never said why. Like because of the sprinklers. And yes itís fully sprinklered. I am glad to be wrong on those issues.

By the way, the plans call for the fire alarm to be ďall devices back to the FACPin 3/4 conduit, no plenum cableĒ itís a class A system. Those words are spelled out on drawings. Would that mean no MC or would Mc cable be equivalent? Yes it canít be free aired wire, but would MC be ok?

Thanks for the responses


Are you talking wiring method in the shaft?


Sent from my iPhone using Tapatalk
DashDingo is offline   Reply With Quote
Old 03-18-2019, 10:12 PM   #6
Senior Member
 
Southeast Power's Avatar
 
Join Date: Jan 2009
Location: Florida
Posts: 17,920
Rewards Points: 8,516
Default

Quote:
Originally Posted by 68Camaro View Post
Ok thanks for replies. The plans call out for elevator wiring to be 2 hr rated. Did not for the other items, so my concern was it was assumed we should. When I asked one or two others, the answer was no. But never said why. Like because of the sprinklers. And yes itís fully sprinklered. I am glad to be wrong on those issues.

By the way, the plans call for the fire alarm to be ďall devices back to the FACPin 3/4 conduit, no plenum cableĒ itís a class A system. Those words are spelled out on drawings. Would that mean no MC or would Mc cable be equivalent? Yes it canít be free aired wire, but would MC be ok?

Thanks for the responses
You have to look in the specs and the shop drawings for the fire alarm system.
The plans are nice but the specifications supersede the plans.
It is going to come down to what the owner paid for and if what they paid for conforms to whatever fire ordinances the local Fire Marshal decides.
Southeast Power is offline   Reply With Quote
Reply

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Owner and project manager 68Camaro New Member Introductions 9 03-15-2019 12:24 AM
Erick Martinez - Project Manager ace1807 New Member Introductions 4 03-21-2018 02:37 PM
Hiring Project Manager/Electrical Estimator Everette WA Robin.v Looking To Hire 0 01-06-2017 02:11 PM
Project Manager pay expectation All4uonline General Electrical Discussion 3 11-28-2016 01:08 AM
Southern Cali- Ontario Project Niguel Electric Looking To Hire 0 01-14-2016 11:19 PM


All times are GMT -4. The time now is 12:57 AM.


Powered by vBulletin® Version 3.8.8
Copyright ©2000 - 2019, vBulletin Solutions, Inc.
Search Engine Optimization by vBSEO 3.6.1
vBulletin Security provided by vBSecurity v2.2.2 (Pro) - vBulletin Mods & Addons Copyright © 2019 DragonByte Technologies Ltd.
User Alert System provided by Advanced User Tagging (Pro) - vBulletin Mods & Addons Copyright © 2019 DragonByte Technologies Ltd.
Our Pro Sites Network
ContractorTalk.com | DrywallTalk.com | HVACSite.com | PaintTalk.com | PlumbingZone.com | RoofingTalk.com