So i've a Y to delta 480.
But i'm not reading anything from phase to ground
this can't be right.....shouldn't it have been corner/center grounded?
Old 01-19-2018, 08:41 PM   #2
Rewards Points: 1,360
Need more info.
nolabama likes this.
Old 01-19-2018, 08:45 PM   #3
Rewards Points: 16,780
where did ya read the voltage ?
did ya read from line to line and line to ground and what the numbers ya hitting ?
Old 01-20-2018, 04:49 AM   #4
Retired Account
line/line is all 480
line to G is 0 , or a few residual volts French One
I'm thinking the secondary isn't make to XO
Thus it can't carry a fault.....am i wrong?
Old 01-20-2018, 06:15 AM   #5
Retired Account
I have an 'ungrounded delta' , (via others) that i'm making straight (no noodle) 480V branch circuits off of
Can anyone validate the grounding in art 250?
Old 01-20-2018, 07:00 AM   #6
Chicken Steve .,
Just be extra carefull with ungrounded delta system they will bite ya pretty hard if you are not aware of this .
Did the service is actually ungrounded delta ? if so they should have a ground fault indenticator lights or others means for ground fault.
Look up in art 250 but there few spots you will have to find it due it will be in at least 3 or 4 spots for sure plus I think it mention in art 310 but not sure due I havent look at nec code book recentally. so expect in few places.
Yes the ungrounded delta can carry single phase fault with out affect the system typically line to ground but line to line fault yes it will either blow the fuse or trip the breaker.
Myself and few other guys in here have allready dealt with ungrounded system it is a pain in arse if not aware at the source.
but if you need single phase load., you will need SDS single phase transfomer and follow the SDS rules on that.
What this unground load is going to be feed for ? motor load or transfomer ?
If you do see the transfomer then did you see how the secondary been hooked ? If so what type of transfomer it was ? typically I useally ran into are isolation or drive transfomer typically 1:1 ratio
Old 01-20-2018, 07:11 AM   #7
Retired Account
Default CS
[quote=frenchelectrican;4703242]Chicken Steve .,
yeah i get that FrenchOne
No, the incoming service is 208/120 3 phase Y , this Xformer sits right next to that main 800A disco, Y to D, then goes into a trough with both voltage disco's mounted above it, (480 & 208/120)
Yeah, been looking , but just can't quite put my finger on the 'letter of code' here.....
I'm unsure how, i get no readings H to G , so i'm lost as to how the fault path occurs back to XO , especially if there is no connection to it
It's in a 250Ksq ft facility with a bunch of starving artists who are all glass blowers, and want me to hook up their furnaces (all straight 480 3 ph)
All i know is it's Y primary D secondary
I haven't taken the cover off to investigate, nor can (or will) i unless i can shut the building down
Now i'm wondering about it's (the Xfomrer's) prim & sec protection as well via 450
I hate walking into someone else's 'effin' mess.....~CS~
Old 01-20-2018, 07:25 AM   #8
Rewards Points: 3,690
The ungrounded system has no grounded conductor. Since none of the conductors are grounded, there's no potential between ground and any of the L1 L2 L3 terminals.
At the first ground fault, you basically have a corner grounded delta rather than an ungrounded delta. You need the ground fault detection to tell you something's wrong.
When the second ground fault occurs, is when it gets ugly.
https://iaeimagazine.org/magazine/20...ly-ungrounded/
chicken steve (01-20-2018)
Old 01-20-2018, 07:37 AM   #9
[quote=chicken steve;4703266]
Originally Posted by frenchelectrican View Post
Chicken Steve .,
FE: Good then you are aware of it.
FE: Look below for more comment I will get both details in one shot.
FE:I dont have the NEC code book with me right now cuz I am sitting on ferry boat now due generator issue. but yes I do recall the NEC did cover at least 4 parts as soon I get the numbers I will posted for ya.
FE:The XO is never used in reverse connection in transfomer at all. either they leave it floating or corner ground it that is the only two way you can advoid the issue with delta secondary.
But if you have grounding conductor in there it will never be tied to XO and it will be a straight shot thru the transfomer housing.
second thing I been wondering about the transfomer size due you mention electric furances what the glass blowers want. that will bite ya so check it ahead of it.
If you did check the transfomer size I can tell you what is the correct OCPD it supposed to be.,
For conventail 75 KVA units the 480 volts side typically be in 90 amp range while 208 side will be 200 amp unless upsized for primary duty which the inrush current may trip the breaker especially if you have 208 primary side.
That based with proper conductor size in there but if differnt size conductor that can change game on that.
Oh I been into other mess pretty often and some case I just dont like it but have to do it ( only if they sign the paper and get it to meet the code.)
Old 01-20-2018, 07:54 AM   #10
Retired Account
Spot on Mr Splatz.....
and yes it's this....
with ref to >>>
250.4 General Requirements for Grounding and Bonding.
(B) Ungrounded Systems.
4>>>
(4) Path for Fault Current. Electrical equipment, wiring, and
other electrically conductive material likely to become ener‐
gized shall be installed in a manner that creates a low-
impedance circuit from any point on the wiring system to the
electrical supply source to facilitate the operation of overcur‐
rent devices should a second ground fault from a different
phase occur on the wiring system
. The earth shall not be
considered as an effective fault-current path.
BUT, there is no >>>
250,21(B) Ground Detectors. Ground detectors shall be installed
Mr Lofland's sign off got me>>>
What are you waiting for?
Regardless of whether a grounded or ungrounded system is employed, both systems will be grounded. Don’t let the term “ungrounded” fool you. As we have discussed in this article, there is nothing “ungrounded” about an ungrounded system. Relax and have another piece of cake.
I think i've got a ligit complaint here.....
Old 01-20-2018, 07:58 AM   #11
Retired Account
[quote=frenchelectrican;4703298]
I'm going to pull off until next week, i'll go next week with some code enlightenment and firepower from you guys,(thank you all!) and come back with a few more specifics on this FrenchOne
I'll be involving my AHJ on this
Can't afford loosing any more tail feathers on this sort of thing.....~CS~
Old 01-20-2018, 08:41 AM   #12
The person who put the transformer in originally didn't know what they were doing, most likely. If this were an industrial facility with a maintenance crew to watch the place, an ungrounded system might be OK. But with hippies and acid - dropping Vermont artists touching the equipment, it's probably best grounded.
Just ground one phase to the case and GEC. Use a Kenny clamp if think you are required to (you're not). Identify the grounded phase conductor white. You treat that phase just like it was a neutral, which means no fuses in that conductor.
Old 01-20-2018, 08:46 AM   #13
MTW
MTW's Avatar
Rewards Points: 7,858
Call an electrician.
macmikeman, nolabama, ppsh and 1 others like this.
The Following User Says Thank You to MTW For This Useful Post:
macmikeman (01-20-2018)
Old 01-20-2018, 08:50 AM   #14
Chicken steve .,
What both spatz and Rephase277 mention very clear and myself I feel what Rephase been talking about and it more common to corner grounded it and with true three phase loads like electric furance they dont affect the CG system at all. it been the same way with electric motors for years.
I have a feeling that someone miss the crictial step when they install the upstep transformer.
splatz (01-20-2018)
Old 01-20-2018, 09:42 AM   #15
Retired Account
yup...
Old 01-20-2018, 09:47 AM   #16
Retired Account
[quote=frenchelectrican;4703522]
Chicken steve .,
I could ground a phase, or introduce a grounding detector system
grounding a ph means i have to run around revisiting different voltages some 480 equipment having control xfomers may not like
a detector system , at least to my understanding, makes it all complaint
Yup
But the ET sparks caught it , and it'll have to come to light for me to continue to pump any 480 circuitry around, which i'm liable for proper grounding of
Old 01-20-2018, 01:01 PM   #17
86 45 20
Southeast Power's Avatar
Rewards Points: 7,868
Your equipment will never know you grounded a corner so, you are good there.
Also, you mentioned OX. Just to recap for visitors that might not read the entire thread. Don't connect anything to OX when you are using a delta wye transformer backwards.
Old 01-20-2018, 01:14 PM   #18
Retired Account
Ok then i'm lost SP....~CS~
Old 01-20-2018, 03:25 PM   #19
yup...
So you're saying you already knew? Why ask then?
Old 01-20-2018, 05:13 PM   #20
Retired Account
No i don't know the best way to deal with this, yes i am asking
Isn't that what this place is for 277?
Delta High leg breaker brother General Electrical Discussion 5 12-23-2017 02:07 PM
4 wire delta & open delta Madmax73 General Electrical Discussion 6 02-01-2017 10:26 AM
Open delta open wye transformer bank Lone Crapshooter Industrial Electrical Forum 15 09-15-2016 01:42 PM
Why is there a netural in Y and not Delta loads? ThatApprentice General Electrical Discussion 12 09-05-2016 06:15 PM
has anyone ever wire a delta to delta transformer? mike883 General Electrical Discussion 13 06-07-2016 07:38 AM