Above ground fuel storage tank - grounding - Electrician Talk - Professional Electrical Contractors Forum
Old Today, 04:39 PM   #1
Rewards Points: 16
Default Above ground fuel storage tank - grounding
Does anybody have run into any code references NEC-NFPA, API referring requirement for grounding above ground DIESEL storage tanks? I have heard arguments that Diesel being higher flash point does not have issues of fires due to static discharge.
Power2engineer is offline   Reply With Quote
Old Today, 05:48 PM   #2
Rewards Points: 860
NEC grounding does not change. If it is diesel fuel it is no longer considered a Cl I Div I area because of the higher flash point.
tmessner is online now   Reply With Quote
Old Today, 09:31 PM   #3
Chief Flunky
Rewards Points: 338
You ground tanks for structural grounding reasons. This is not NEC. See NFPA 780, or the API standards for storage tanks.
Diesel does not have a vapor problem. Drop a match in it and it puts it out. Also it is not a “dry” liquid...no static charge from transfers. So you ground like you do a building, nothing special for the fuel.
Tags
api, ast, diesel, grounding, nec