Old 03-07-2019, 07:38 AM   #1
Junior Member
 
Join Date: Mar 2019
Posts: 5
Rewards Points: 10
Default Burning out of return side

I’ve come across a few circuits in Berkeley that have been failing on the return side of 120 volt receptacles? Arcing enough to melt the face of device, in a recent kitchen remodel 2006? All inspected but failing where 1500 watt appliance have been used not old appliances? I believe all were 20amp leviton devices, all new Romex circuits? Possibly just poor workmanship? No loose connections that I’ve found?
tomjahnson is offline   Reply With Quote
Join Contractor Talk

Join the #1 Electrician Forum Today - It's Totally Free!

ElectricianTalk.com - Are you a Professional Electrical Contractor? If so we invite you to join our community and see what it has to offer. Our site is specifically designed for you and it's the leading place for electricians to meet online. No homeowners asking DIY questions. Just fellow tradesmen who enjoy talking about their business, their trade, and anything else that comes up. No matter what your specialty is you'll find that ElectricianTalk.com is a great community to join. Best of all it's totally free!

Join ElectricianTalk.com - Click Here JOIN FOR FREE


Warning: The topics covered on this site include activities in which there exists the potential for serious injury or death. ElectricianTalk.com DOES NOT guarantee the accuracy or completeness of any information contained on this site. Always use proper safety precaution and reference reliable outside sources before attempting any construction or remodeling task!

Sponsored Links
Advertisement
 
Old 03-07-2019, 08:09 AM   #2
Sentimental Mental
 
CTshockhazard's Avatar
 
Join Date: Aug 2009
Location: CT
Posts: 986
Rewards Points: 1,456
Default

Arcing, enough to melt the face of a device, is a connection issue.


Arcs happen between gaps in conductive surfaces that have current flowing across them.
__________________
.
__________________________________________________

Just to be absolutely clear...
I didn't say anything about nothing to nobody.
CTshockhazard is offline   Reply With Quote
The Following 2 Users Say Thank You to CTshockhazard For This Useful Post:
tomjahnson (03-07-2019), VELOCI3 (08-19-2019)
Old 03-07-2019, 08:56 AM   #3
Junior Member
 
Join Date: Mar 2019
Posts: 5
Rewards Points: 10
Default

Thanks
tomjahnson is offline   Reply With Quote
Sponsored Links
Advertisement
 
Old 03-07-2019, 11:19 AM   #4
Senior Member
 
just the cowboy's Avatar
 
Join Date: Sep 2013
Location: Colorado
Posts: 1,635
Rewards Points: 16
Default

Are they backstabbed? Quite common.
__________________
A cowboy may get thrown down, but he always gets up and walks forward and don't look back at what thru him.
just the cowboy is online now   Reply With Quote
The Following User Says Thank You to just the cowboy For This Useful Post:
VELOCI3 (08-19-2019)
Old 03-07-2019, 02:10 PM   #5
Old Grumpy Bastard
 
MechanicalDVR's Avatar
 
Join Date: Dec 2007
Location: "Old Dominion"
Posts: 59,572
Rewards Points: 1,556
Default

Quote:
Originally Posted by tomjahnson View Post
I’ve come across a few circuits in Berkeley that have been failing on the return side of 120 volt receptacles? Arcing enough to melt the face of device, in a recent kitchen remodel 2006? All inspected but failing where 1500 watt appliance have been used not old appliances? I believe all were 20amp leviton devices, all new Romex circuits? Possibly just poor workmanship? No loose connections that I’ve found?
Curious, where are you from that you use the term "return side"?
circuitman1 and MikeFL like this.
__________________
I'm as Christian as possible in the times we live in.

Always just a stallion in a china shop
MechanicalDVR is offline   Reply With Quote
Old 03-07-2019, 02:47 PM   #6
Senior Member
 
Join Date: Mar 2013
Location: saluda,s.c.
Posts: 1,012
Rewards Points: 636
Default

you need to fill out your profile, or this thread will be locked!
John Valdes likes this.
circuitman1 is offline   Reply With Quote
Old 03-07-2019, 03:27 PM   #7
Senior Member
 
MikeFL's Avatar
 
Join Date: Apr 2016
Location: The Sunshine State
Posts: 5,463
Rewards Points: 3,024
Default

Quote:
Originally Posted by MechanicalDVR View Post
Curious, where are you from that you use the term "return side"?
I think he's in Cali.

Berkley?
__________________
Michael Gookin, President
GPS Timers

To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts.

(833) GPS-TIME
MikeFL is online now   Reply With Quote
Old 03-07-2019, 05:33 PM   #8
Modérateur
 
frenchelectrican's Avatar
 
Join Date: Mar 2007
Location: Philippines
Posts: 8,635
Rewards Points: 16,782
Default

To OP .,,

are you legit electrician or not ? because the key word is return line that is something we genrally dont say it.

I will give you 24 hours to come up with info otherwise this thread will be locked.
__________________
Bleu est beau.
frenchelectrican is offline   Reply With Quote
The Following User Says Thank You to frenchelectrican For This Useful Post:
John Valdes (08-12-2019)
Old 03-07-2019, 11:04 PM   #9
Old Grumpy Bastard
 
MechanicalDVR's Avatar
 
Join Date: Dec 2007
Location: "Old Dominion"
Posts: 59,572
Rewards Points: 1,556
Default

Quote:
Originally Posted by MikeFL View Post
I think he's in Cali.

Berkley?
I've spoken to many Californians and never heard it phrased like that before.

You?
circuitman1 likes this.
__________________
I'm as Christian as possible in the times we live in.

Always just a stallion in a china shop
MechanicalDVR is offline   Reply With Quote
Old 03-07-2019, 11:37 PM   #10
Senior Member
 
MikeFL's Avatar
 
Join Date: Apr 2016
Location: The Sunshine State
Posts: 5,463
Rewards Points: 3,024
Default

Never.
MechanicalDVR likes this.
__________________
Michael Gookin, President
GPS Timers

To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts.

(833) GPS-TIME
MikeFL is online now   Reply With Quote
Old 03-08-2019, 12:55 AM   #11
Senile Member
 
macmikeman's Avatar
 
Join Date: Jan 2007
Location: Honolulu
Posts: 27,148
Rewards Points: 16,655
Default

Wait a minute fella's ........... maybe a fault on a zig zag primary came up the GE and got into the neutral bus............. Nah..
__________________
Just days before China unveiled a nuclear weapon that can "strike the US within 30 minutes with ten warheads" as part of a giant military parade, US Major General Lori Reynolds announced she's declaring "diversity" is a "warfighting necessity" which will help America defeat the more homogeneous nations of China and Russia.
macmikeman is offline   Reply With Quote
Old 03-08-2019, 09:15 AM   #12
Old Grumpy Bastard
 
MechanicalDVR's Avatar
 
Join Date: Dec 2007
Location: "Old Dominion"
Posts: 59,572
Rewards Points: 1,556
Default

Quote:
Originally Posted by macmikeman View Post
Wait a minute fella's ........... maybe a fault on a zig zag primary came up the GE and got into the neutral bus............. Nah..
I haven't heard of a primary Zig Zag fault since high school!
circuitman1 and MikeFL like this.
__________________
I'm as Christian as possible in the times we live in.

Always just a stallion in a china shop
MechanicalDVR is offline   Reply With Quote
Old 03-10-2019, 08:50 PM   #13
Pull my wire
 
Join Date: May 2015
Location: Montreal-Vancouver
Posts: 294
Rewards Points: 246
Default

Must be french canadian, coz we say that all the time in french "sur le retour du circuit", aka on the return side. But no Berkeley around here and that does sound like a Cali city.

Sounds like bad connection from poor workmanship and using cheap appliances with tiny cords for a little bit too long.
MechanicalDVR and MikeFL like this.
David C is offline   Reply With Quote
Old 08-12-2019, 03:27 PM   #14
Junior Member
 
Join Date: Aug 2019
Posts: 18
Rewards Points: 42
Default

Arcing, enough to melt the face of a device, is a connection issue.


Arcs happen between gaps in conductive surfaces that have current flowing across them.
fmwowol is offline   Reply With Quote
Old 08-12-2019, 04:19 PM   #15
Band Member
 
emtnut's Avatar
 
Join Date: Mar 2015
Location: Eastern Ontario
Posts: 5,840
Rewards Points: 1,258
Default

Quote:
Originally Posted by CTshockhazard View Post
Arcing, enough to melt the face of a device, is a connection issue.


Arcs happen between gaps in conductive surfaces that have current flowing across them.
Quote:
Originally Posted by fmwowol View Post
Arcing, enough to melt the face of a device, is a connection issue.


Arcs happen between gaps in conductive surfaces that have current flowing across them.
Arcing, enough to melt the face of a device, is a connection issue.


Arcs happen between gaps in conductive surfaces that have current flowing across them.
telsa likes this.
__________________
_____________________________________
Your Mother was a hamster, and your father smells of Elderberries. ... Now go away, or I shall taunt you a second time
To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts.
emtnut is offline   Reply With Quote
Old 08-12-2019, 04:23 PM   #16
Senior Member
 
Join Date: May 2015
Location: Sacramento, California
Posts: 13,976
Rewards Points: 26,198
Default

Obviously, you can't say that enough.
MechanicalDVR likes this.
telsa is offline   Reply With Quote
Old 08-12-2019, 05:16 PM   #17
Senior Member
 
HertzHound's Avatar
 
Join Date: Jan 2019
Location: East coast
Posts: 540
Rewards Points: 902
Default

Quote:
Originally Posted by telsa View Post
Obviously, you can't say that enough.
I wonder what his thoughts are on 14 gauge pigtails on 12 gauge wire.
__________________
“Why say lot words when few words do trick”
HertzHound is online now   Reply With Quote
Old 08-13-2019, 10:10 AM   #18
Senior Member
 
Join Date: Oct 2012
Location: Alberta Rockies
Posts: 2,725
Rewards Points: 3,808
Default

Quote:
Originally Posted by CTshockhazard View Post
Arcing, enough to melt the face of a device, is a connection issue.


Arcs happen between gaps in conductive surfaces that have current flowing across them.
Quote:
Originally Posted by fmwowol View Post
Arcing, enough to melt the face of a device, is a connection issue.


Arcs happen between gaps in conductive surfaces that have current flowing across them.
5 months for your fan @CTshockhazard.. lol..
@MechanicalDVR
glen1971 is offline   Reply With Quote
Old 08-19-2019, 06:39 PM   #19
Junior Member
 
Join Date: Aug 2019
Location: Georgia
Posts: 1
Rewards Points: 2
Default

Sounds like the system is out of balance by at least 20 wc
Nobbler is offline   Reply With Quote
Old 08-19-2019, 09:28 PM   #20
Member
 
Join Date: Aug 2019
Location: NY
Posts: 73
Rewards Points: 90
Default

We have a saying here in NY about Rube Goldberg type wiring. Well we either call it that or California wiring.

But seriously it sounds like you have a phantom phase on the downstream neutral.
Grounded-B likes this.

Last edited by VELOCI3; 08-19-2019 at 09:37 PM.
VELOCI3 is offline   Reply With Quote
Reply

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
How much do I charge? (side job) JasonCo General Electrical Discussion 96 07-04-2018 09:56 AM
Harmonics on load side of transformer Flex277 Commercial Electrical Forum 17 03-04-2018 09:31 PM
VFD-Line Side Readings AaronJ PLCs, VFDs, Motors and Controls 7 10-20-2017 02:32 PM
Line and Load side? JasonCo General Electrical Discussion 7 04-05-2017 12:09 AM


All times are GMT -4. The time now is 08:57 AM.


Powered by vBulletin® Version 3.8.8
Copyright ©2000 - 2019, vBulletin Solutions, Inc.
Search Engine Optimization by vBSEO 3.6.1
vBulletin Security provided by vBSecurity v2.2.2 (Pro) - vBulletin Mods & Addons Copyright © 2019 DragonByte Technologies Ltd.
User Alert System provided by Advanced User Tagging (Pro) - vBulletin Mods & Addons Copyright © 2019 DragonByte Technologies Ltd.
Our Pro Sites Network
ContractorTalk.com | DrywallTalk.com | HVACSite.com | PaintTalk.com | PlumbingZone.com | RoofingTalk.com