I have 8 elevators on my job. Section 38-024(1) of the CEC says a separate branch circuit for an elevator pit. Is this interpreted as 1 cct.per pit? Engineers drawings show a group of 4 pits with 4 of the receptacles on one branch cct. and all 4 pit lights sharing another cct. I interpret this rule as 1 lighting cct and 1 receptacle cct. per pit.
johnniekayak is offline   Reply With Quote
Old 11-06-2019, 03:01 PM   #2
MikeFL's Avatar
Rewards Points: 844
What did the engineer say when you called him?
Michael Gookin, President
GPS Timers
(833) GPS-TIME
Old 11-13-2019, 08:40 PM   #3
Beam Me Up Scotty
Kevin_Essiambre's Avatar
Rewards Points: 410
Are you the Licenced electrician or an apprentice? I cannot tell from your profile because it hasn't been filled out...
It says separate branch circuit for an elevator pit... the way that you are interpreting it, for your 8 pits, you'll need 16 circuits... as MikeFL said, what did the engineer say?
16 circuits for 8 elevator pits? Man, I hope you're installing 1500 watt lights in each pit... Call the Engineer or ask your boss...
Vote Kevin for Moderator!
Old 11-14-2019, 01:35 AM   #4
HertzHound's Avatar
Rewards Points: 1,358
In the NEC the pit light can’t be on the same circuit as the pit receptacle. Usually three circuits when you add in the sump pump. Maybe CEC is similar?
I don’t think we have a code on limiting the separate circuits to one pit. So lighting would share a circuit, receptacle would Share a circuit and pumps would have dedicated circuits. Your sealed drawings seem to follow our code rules. I would just follow the drawings.
The machine room also gets its own receptacle circuit.
<<<< CHIP ME >>>>Not
Old 11-14-2019, 01:55 AM   #5
HertzHound's Avatar
Just for comparison:
620.22 Branch Circuits for Car Lighting, Receptacle(s), Ventilation, Heating, and Air-Conditioning.
(A)Car Light Source.
A separate branch circuit shall supply the car lights, receptacle(s), auxiliary lighting power source, and ventilation on each elevator car. The overcurrent device protecting the branch circuit shall be located in the elevator machine room or control room/machinery space or control space.
620.23 Branch Circuits for Machine Room or Control Room/ Machinery Space or Control Space Lighting and Receptacle(s).
(A)Separate Branch Circuits.
The branch circuit(s) supplying the lighting for machine rooms, control rooms, machinery spaces, or control spaces shall be separate from the branch circuit(s) supplying the receptacle(s) in those places. These circuits shall supply no other loads.
620.24 Branch Circuit for Hoistway Pit Lighting and Receptacles.
Separate branch circuits shall supply the hoistway pit lighting and receptacles.
Kevin_Essiambre likes this.
Old 11-14-2019, 08:57 AM   #6
Coffee drinking member
Wirenuting's Avatar
Rewards Points: 7,396
Is it a common pit or individual shafts?
Old 11-14-2019, 09:08 AM   #7
Rewards Points: 1,881
All I know about elevators is that elevator inspectors are free to write their own rules and electrical code is meaningless to them.
Old 11-14-2019, 10:03 AM   #8
Rewards Points: 778
I would think that if the NEC intended a separate circuit for each pit was required, then it would use the term, " Individual" branch circuit or "dedicated". I know the intent is not to have the receptacle and light together so that the service worker is not in the dark if he trips out the breaker while using the receptacle.
I concur with the previous comment, Ask the engineer.
Old 11-14-2019, 03:52 PM   #9
Awg-Dawg's Avatar
Rewards Points: 726
I had one tell me over and over that a pit is a wet location.
But when I asked what makes it a wet location , he said the pit makes it one and that I had to use raintight fittings and in use covers.
I asked him if he’d seen sumps in a basement of dwellings, he said yes but those are different.
I feel sorry for people who don't drink, when they wake up in the morning, that's the best they will feel all day.
Awg-Dawg is offline   Reply With Quote