Default Grouping of disconnects for service

I am doing an addittion with 150A MB panel and the existing part of the house has a 200A MB panel. I screwed up when I got everything and got 65' of seu for the 150 to go to the meter, but since the panels aren't together I have to group to mb enclosures outside. Now that 65' or most of that 65' is useless since I have to run ser so I can have the insulated neutral. My question is how far apart can I have the the mb enclosures for it still to be acceptable if there both outside on the same wall?

The one for the 200A will be near the meter, but I would like to put the 150A as far away as I can in order to use most of the seu and not have to get as much ser.
ikeberg9 is offline   Reply With Quote
Join Contractor Talk

Join the #1 Electrician Forum Today - It's Totally Free!

ElectricianTalk.com - Are you a Professional Electrical Contractor? If so we invite you to join our community and see what it has to offer. Our site is specifically designed for you and it's the leading place for electricians to meet online. No homeowners asking DIY questions. Just fellow tradesmen who enjoy talking about their business, their trade, and anything else that comes up. No matter what your specialty is you'll find that ElectricianTalk.com is a great community to join. Best of all it's totally free!

Join ElectricianTalk.com - Click Here JOIN FOR FREE


Warning: The topics covered on this site include activities in which there exists the potential for serious injury or death. ElectricianTalk.com DOES NOT guarantee the accuracy or completeness of any information contained on this site. Always use proper safety precaution and reference reliable outside sources before attempting any construction or remodeling task!

Sponsored Links
Advertisement
 
Old 12-21-2010, 09:03 PM   #2
Fried Bologna um um good!
 
jwjrw's Avatar
 
Join Date: Jan 2010
Location: nc
Posts: 8,094
Default

As far as your AHJ allows you to have them apart.
__________________
The more I learn the less I seem to know......
To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts.
jwjrw is offline   Reply With Quote
Old 12-21-2010, 09:05 PM   #3
child please.....
 
NolaTigaBait's Avatar
 
Join Date: Oct 2008
Location: Hack City, USA aka New Orleans
Posts: 5,311
Rewards Points: 14
Default

The NEC doesn't specify a distance...I'd ask the inspector like jw said.
__________________
REMOVED
NolaTigaBait is offline   Reply With Quote
Sponsored Links
Advertisement
 
Old 12-21-2010, 11:49 PM   #4
Junior Member
 
Join Date: Jan 2010
Location: maryland
Posts: 19
Rewards Points: 10
Default

Ya that's what I figured. Thanks and I will post what they tell me.
ikeberg9 is offline   Reply With Quote
Old 12-22-2010, 02:11 AM   #5
Senior Member
 
Join Date: Sep 2009
Location: WA
Posts: 4,066
Rewards Points: 2,000
Default

They have to be in the same room... I really don't see it as a problem but the NEC doesn't agree with me..
nitro71 is offline   Reply With Quote
Old 12-22-2010, 09:00 AM   #6
evil bastard
 
mcclary's electrical's Avatar
 
Join Date: Feb 2009
Location: State of Euphoria
Posts: 15,771
Rewards Points: 746
Default

Quote:
Originally Posted by ikeberg9 View Post
I am doing an addittion with 150A MB panel and the existing part of the house has a 200A MB panel. I screwed up when I got everything and got 65' of seu for the 150 to go to the meter, but since the panels aren't together I have to group to mb enclosures outside. Now that 65' or most of that 65' is useless since I have to run ser so I can have the insulated neutral. My question is how far apart can I have the the mb enclosures for it still to be acceptable if there both outside on the same wall?

The one for the 200A will be near the meter, but I would like to put the 150A as far away as I can in order to use most of the seu and not have to get as much ser.

Is the addition attached? That is not a service disconnect, and does not have to be grouped with your original service disconnect.
mcclary's electrical is offline   Reply With Quote
Old 12-22-2010, 09:38 AM   #7
child please.....
 
NolaTigaBait's Avatar
 
Join Date: Oct 2008
Location: Hack City, USA aka New Orleans
Posts: 5,311
Rewards Points: 14
Default

Quote:
Originally Posted by mcclary's electrical View Post
Is the addition attached? That is not a service disconnect, and does not have to be grouped with your original service disconnect.
Good point...I guess I read it as if there were 2 meters(service disconnects) for some reason.
__________________
REMOVED
NolaTigaBait is offline   Reply With Quote
Old 12-22-2010, 04:44 PM   #8
Junior Member
 
Join Date: Jan 2010
Location: maryland
Posts: 19
Rewards Points: 10
Default

Yes the addition is attached. I would be mounting the enclosed breakers on the outside wall near the meter. The first 200A panel is right by the meter. The wall out there is about 35'-40' long and the meter is on one side and the new 150A is right near the other end of that wall. After reading 230.70 is it really necessary to have a way of disconnecting the service entrance conductors on both panels in one central location, since each panel is a main breaker panel.
ikeberg9 is offline   Reply With Quote
Old 12-22-2010, 06:18 PM   #9
evil bastard
 
mcclary's electrical's Avatar
 
Join Date: Feb 2009
Location: State of Euphoria
Posts: 15,771
Rewards Points: 746
Default

Quote:
Originally Posted by ikeberg9 View Post
Yes the addition is attached. I would be mounting the enclosed breakers on the outside wall near the meter. The first 200A panel is right by the meter. The wall out there is about 35'-40' long and the meter is on one side and the new 150A is right near the other end of that wall. After reading 230.70 is it really necessary to have a way of disconnecting the service entrance conductors on both panels in one central location, since each panel is a main breaker panel.


Are you double lugging the meter?

If not, you DO NOT have two sets of service entrance conductors, and you disconnect for the addition does not have to be grouped or anywhere near the service disconnect.
mcclary's electrical is offline   Reply With Quote
Reply

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Bargain Disconnects at The HD crazyboy General Electrical Discussion 7 06-02-2010 01:57 AM
100 amp disconnects electagb Electrician Swap 0 01-13-2010 03:36 PM
Fused A/C disconnects user4818 NEC Code Forum 117 11-20-2009 12:02 AM
Luminare Disconnects jbfan General Electrical Discussion 3 06-26-2008 02:46 PM
Code for disconnects at UPS brucelaird Services and Service Equipment 0 03-20-2008 05:45 PM


All times are GMT -4. The time now is 02:53 AM.


Powered by vBulletin® Version 3.8.8
Copyright ©2000 - 2020, vBulletin Solutions, Inc.
Search Engine Optimization by vBSEO 3.6.1
vBulletin Security provided by vBSecurity v2.2.2 (Pro) - vBulletin Mods & Addons Copyright © 2020 DragonByte Technologies Ltd.
User Alert System provided by Advanced User Tagging (Pro) - vBulletin Mods & Addons Copyright © 2020 DragonByte Technologies Ltd.
Our Pro Sites Network
ContractorTalk.com | DrywallTalk.com | HVACSite.com | PaintTalk.com | PlumbingZone.com | RoofingTalk.com