I am typically all residential, but this shouldn't be a problem. The business owner said the salesperson told him it would require a 60 amp breaker. I'm wiring an Ingersoll Rand TS4N5 air Compressor. The plate says 230V and 21.5 FLA. Why would I need a 60 amp breaker?
It's going to be placed within 25' of the breaker box, so I was going to put a double pole 30 and use #10. Even if I did 1 1/2% it would be a 40 amp breaker. How should I wire this thing? Thanks so much! -John
Ingersoll Rand Air Compressor wiring-img_6486.jpg   Ingersoll Rand Air Compressor wiring-img_6485.jpg   Ingersoll Rand Air Compressor wiring-img_6487.jpg
bantar1000 is offline   Reply With Quote
Old 05-13-2019, 07:01 PM   #2
Rewards Points: 5,716
What is the actual current at 220 volts (which is probably what you have) and what is the in-rush on starting?
Cheers
John
Old 05-13-2019, 07:42 PM   #3
Knotted Ropes Skeery
CoolWill's Avatar
Rewards Points: 1,814
You can size the breaker up to 250% of the FLA, but just because you can doesn't mean you should. A 40 amp breaker on #10 wire should be OK.
bantar1000 likes this.
Old 05-13-2019, 09:39 PM   #4
jw0445's Avatar
Rewards Points: 1,980
I have that compressor in my shop. I ran 10's on a 40. It kept tripping out once it had pressure in it. I ended up running 6 on a 60 amp breaker and never looked back. P.S. It is a great compressor.
splatz and John R like this.
Old 05-13-2019, 10:35 PM   #5
Cow
Rewards Points: 5,210
#10 thhn on a 40.
Or
#8 Romex on a 40.
I'm not sure if you're piping it or what...
Old 05-14-2019, 12:15 AM   #6
Rewards Points: 916
If the tag says minimum circuit ampacity ____. Maximum CB or fuse size, then you use that. If not then I you have to use NEC 430.248 and add 25% regardless of what the tag says. Is the building 208 volts or 240 volts.
FYI : A NEMA motor rated hp is a measure of work while an IEC motor hp is a measure of how much energy it uses. That is why a NEMA 5 hp motor is bigger and draws more amperes than a IEC motor.
Old 05-14-2019, 03:37 AM   #7
Rewards Points: 8,049
Depends if it has an unloader or not. If it don't, it'll start under full head pressure, and the 60a. would be my choice.
Old 05-14-2019, 04:17 PM   #8
Rewards Points: 938
Air compressors notoriously start under a very heavy load. This is normal, and also why they don't repeatedly cycle. You can use a smaller breaker and swap it out if you get nuisance trips, but it sounds like your sales rep has seen this before and knows these units take a good 300% to start.
Old 05-16-2019, 09:06 PM   #9
Jlarson's Avatar
Rewards Points: 4,292
I usually throw 10's and a 60 amp at those compressors.