Question Transformer Primary Conductors Calculation

Hey Guys,

We have a Solar system installed with the following specs:
- Voltage: 480 V
- Current: 1080 A

This is fed into the secondary of the 1000 kVA transformer with 4kV on the primary whose spec. is:
kVA= (1.732 x 480 x 1080)/1000 = 897.895 kVA (1000 kVA is used)

From this the primary current will be:
I = 897.995*1000/1.732*4000 = 129.6 A

The primary is interconnected to the grid

The POCO asked us to use a 2/0 wire for the primary, but I wanted to verify this so, Can someone please provide a step by step process to calculate the conductor size for the primary according to NEC?

Thanks in Advance
The_Electrician is offline   Reply With Quote
Join Contractor Talk

Join the #1 Electrician Forum Today - It's Totally Free!

ElectricianTalk.com - Are you a Professional Electrical Contractor? If so we invite you to join our community and see what it has to offer. Our site is specifically designed for you and it's the leading place for electricians to meet online. No homeowners asking DIY questions. Just fellow tradesmen who enjoy talking about their business, their trade, and anything else that comes up. No matter what your specialty is you'll find that ElectricianTalk.com is a great community to join. Best of all it's totally free!

Join ElectricianTalk.com - Click Here JOIN FOR FREE


Warning: The topics covered on this site include activities in which there exists the potential for serious injury or death. ElectricianTalk.com DOES NOT guarantee the accuracy or completeness of any information contained on this site. Always use proper safety precaution and reference reliable outside sources before attempting any construction or remodeling task!

Sponsored Links
Advertisement
 
Old 05-23-2019, 04:13 PM   #2
Senior Member
 
Join Date: Nov 2012
Location: Philly/NJ
Posts: 560
Rewards Points: 888
Default

you gota use what the POCO wants, they have their own guidelines for services and they do not necessarily use the NEC.

around here u can use #2 awg Cooper MV cable for that load.
Tonedeaf is offline   Reply With Quote
The Following User Says Thank You to Tonedeaf For This Useful Post:
The_Electrician (05-23-2019)
Old 05-23-2019, 04:34 PM   #3
Junior Member
 
Join Date: Apr 2019
Location: USA
Posts: 7
Rewards Points: 14
Default

Quote:
Originally Posted by Tonedeaf View Post
you gota use what the POCO wants, they have their own guidelines for services and they do not necessarily use the NEC.

around here u can use #2 awg Cooper MV cable for that load.
Hey, Thank you, did you come up with #2 using 310.15(B)(16) 90 degree Temp.? Also, do I have to install a primary side protection for even if I am connecting directly to the utility line?
The_Electrician is offline   Reply With Quote
Sponsored Links
Advertisement
 
Old 05-23-2019, 04:46 PM   #4
Senior Member
 
Join Date: Nov 2012
Location: Philly/NJ
Posts: 560
Rewards Points: 888
Default

Quote:
Originally Posted by The_Electrician View Post
Hey, Thank you, did you come up with #2 using 310.15(B)(16) 90 degree Temp.? Also, do I have to install a primary side protection for even if I am connecting directly to the utility line?


we have to use 15KV cable and terminations for 4160V....utililites around here don't want to stock 5kv stuff and they are trying to phase out 4160.

15KV XPLE #2 awg cooper xple or epr is good for 150-165 amps in duct. I think its 90 table
The_Electrician likes this.
Tonedeaf is offline   Reply With Quote
Old 05-23-2019, 05:04 PM   #5
Junior Member
 
Join Date: Apr 2019
Location: USA
Posts: 7
Rewards Points: 14
Default

Quote:
Originally Posted by Tonedeaf View Post
we have to use 15KV cable and terminations for 4160V....utililites around here don't want to stock 5kv stuff and they are trying to phase out 4160.

15KV XPLE #2 awg cooper xple or epr is good for 150-165 amps in duct. I think its 90 table
Now I got it!, I couldn't find table 90 is it in article 310?
The_Electrician is offline   Reply With Quote
Old 05-23-2019, 05:15 PM   #6
Senior Member
 
Join Date: Nov 2012
Location: Philly/NJ
Posts: 560
Rewards Points: 888
Default

https://www.mysouthwire.com/medias/s...4088417310.pdf

here's tables from southwire

90 degree induct #2 good for 150 amps
Tonedeaf is offline   Reply With Quote
The Following User Says Thank You to Tonedeaf For This Useful Post:
The_Electrician (05-23-2019)
Old 05-23-2019, 05:25 PM   #7
Junior Member
 
Join Date: Apr 2019
Location: USA
Posts: 7
Rewards Points: 14
Default

Quote:
Originally Posted by Tonedeaf View Post

here's tables from southwire

90 degree induct #2 good for 150 amps
Thanks man, appreciate it. I have one more doubt, Do I have to have a primary protection for the transformer like a service disconnect even if I connect the primary of the transformer directly to 4kV line of the utility?
The_Electrician is offline   Reply With Quote
Reply

Tags
#primary, #transformer

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
3 Phase Transformer load calculation TOOL_5150 Commercial Electrical Forum 6 06-26-2017 11:56 AM
Pull Box size calculation - Parallel conductors TOOL_5150 NEC Code Forum 7 03-20-2017 11:08 PM
Transformer Primary protection rossi32s Industrial Electrical Forum 5 11-08-2016 12:58 AM
Transformer Calculation Aegis General Electrical Discussion 2 06-01-2016 02:39 PM
Three phase Wye Transformer KVA calculation/ Homework typo? JasonCo General Electrical Discussion 3 03-11-2016 07:02 PM


All times are GMT -4. The time now is 04:12 AM.


Powered by vBulletin® Version 3.8.8
Copyright ©2000 - 2019, vBulletin Solutions, Inc.
Search Engine Optimization by vBSEO 3.6.1
vBulletin Security provided by vBSecurity v2.2.2 (Pro) - vBulletin Mods & Addons Copyright © 2019 DragonByte Technologies Ltd.
User Alert System provided by Advanced User Tagging (Pro) - vBulletin Mods & Addons Copyright © 2019 DragonByte Technologies Ltd.
Our Pro Sites Network
ContractorTalk.com | DrywallTalk.com | HVACSite.com | PaintTalk.com | PlumbingZone.com | RoofingTalk.com