On site now: have a 20A 120V single phase dedicated circuit with 10AWG conductors. Off that are 2 12A nameplate rated pieces of equipment connected with 12AWG flexible cord drops.

They are tripping the breaker would it be 2008 NEC compliant to increase the ampacity to 30A?
 

· Administrator
Retired EC
Joined
·
24,975 Posts
On site now: have a 20A 120V single phase dedicated circuit with 10AWG conductors. Off that are 2 12A nameplate rated pieces of equipment connected with 12AWG flexible cord drops.

They are tripping the breaker would it be 2008 NEC compliant to increase the ampacity to 30A?
I would think not but it may depend on the nameplate & the type of equipment
 

· Registered
Joined
·
15 Posts
Discussion Starter · #6 ·
They are a table top heat sealer for shrink wrapping. 115V 12A nameplate rated per machine. 2 machines connected to the 10AWG feed connected to two 12AWG flexible cords in the junction box. 10AWG on a 20A breaker.
 

· Registered
Joined
·
11,734 Posts
They are a table top heat sealer for shrink wrapping. 115V 12A nameplate rated per machine. 2 machines connected to the 10AWG feed connected to two 12AWG flexible cords in the junction box. 10AWG on a 20A breaker.
Any disconnects to them? If there was a fused disconnect for each one I would bump up to 30 in a heart beat.
 

· Premium Member
Licensed Electrical Contractor
Joined
·
11,733 Posts
Any disconnects to them? If there was a fused disconnect for each one I would bump up to 30 in a heart beat.
Agree.

If they are plug in with 15 or 20A plugs/receptacles/caps you definitely CANNOT do it.
This is why all the details are important. Just saying you have two #12 drops is not enough.
 
  • Like
Reactions: micromind

· Moderator
Estwing magic
Joined
·
28,212 Posts
They are a table top heat sealer for shrink wrapping. 115V 12A nameplate rated per machine. 2 machines connected to the 10AWG feed connected to two 12AWG flexible cords in the junction box. 10AWG on a 20A breaker.
You have two 12A machines connected to a single 20A circuit? Now I understand why it's tripping. Carry on, gentlemen...
 

· Senile Member
I make all the electrons line up for their Flu shots
Joined
·
37,482 Posts
Branch circuit turned into feeders for a new sub panel with two new 20 amp circuit breakers controlling the two loads attached to the panel. Ace hardware sells those two circuit nema 1 loadcenters. This may not sit perfectly with code but imho the more overcurrent protection the merryier in the case of machinery.
 

· Registered
Joined
·
15 Posts
Discussion Starter · #14 ·
Exactly my thought 24 amps of potential current tripping the breaker. Funny thing it's been ok since they put it in over a year ago.

Only disconnect is the breaker at the panel. What code section is being used for using disconnects for the two drops ?
 

· Administrator
Retired EC
Joined
·
24,975 Posts
A 20A circuit will carry 24A for quite a while.
If these machine are running all the time it will trip eventually.

I would add a fused disconnect for each unit and then use the 30 amp feeder as someone suggested. Otherwise the #12 on the circuit will not allow a 30 amp overcurrent protective device
 

· Registered
Joined
·
11,734 Posts
Branch circuit turned into feeders for a new sub panel with two new 20 amp circuit breakers controlling the two loads attached to the panel. Ace hardware sells those two circuit nema 1 loadcenters. This may not sit perfectly with code but imho the more overcurrent protection the merryier in the case of machinery.
Code would actually recommended that over anything else.





Exactly my thought 24 amps of potential current tripping the breaker. Funny thing it's been ok since they put it in over a year ago.

Only disconnect is the breaker at the panel. What code section is being used for using disconnects for the two drops ?
Don't reuse the breaker, good chance its ruined from repeated overheating, tripping and resetting.

I don't know about the NEC but if those machines are in an industrial facility they should have a disconnect within sight
to satisfy safety requirements. If not a red push button with a shunt trip feeder breaker...

To keep it simple drop a 2 space QO panel from HD and call it good:

http://www.homedepot.com/p/Square-D...L30SCP/100157760?N=bm0u?Ns=P_REP_PRC_MODE%7C0#
 

· Moderator
Estwing magic
Joined
·
28,212 Posts
Exactly my thought 24 amps of potential current tripping the breaker. Funny thing it's been ok since they put it in over a year ago.

Only disconnect is the breaker at the panel. What code section is being used for using disconnects for the two drops ?
Your breaker could be getting tired and trip time can decrease after multiple trips.
 

· Registered
Joined
·
15 Posts
Discussion Starter · #19 ·
Yes breakers a are designed to carry current rates above the marking on the breaker. I have seen a 20A carry 21A continuous but of course not NEC compliant.

Looking at the wiring here it seems like the best course of action will be pulling another conductor here from the panel for accessibility reasons. Got no where to mount a disconnect except where the drop is off the ceiling 16ft overhead.
 