I would say yes.
The 125a CB protects the feeder (assuming it's sized correctly).
The 200a CB would provide a separate structure main disconnect.
The 200a buss would be able to handle an excess load from 2 sources, the 125a main and the PV source. Again I don't know what the solar output is, but am guessing it's less than 75a.