210.21 (B)(3) tells us we can use a 15 receptacle on a 20 amp circuit
now 210.21 (B)(2)table shows if you use a 15 amp receptacle on a 20 amp receptacle you are allowed max 12 amps of plug and cord load on that circuit when you have 2 or more receptacles...correct?
Does this mean continuous 12 amps or 12 amps period?
What about all these 13 amp cord and plug power tools? Is that technically not allowed? Or is it allowed because the 13 amps it could reach is non continuous?