Hi guys, just wanted a quick advice from you about this problem.
So at my new job there is a motor that shorted twice that i cant confirm because the other electrician is gone.
And that motor is a 7.5hp 575v 2 speed star delta for a cooling tower.
I could blame the motor but i found 2 weird thing about the control of it
1st there is no timer or mecanical lock between the contactors used for the low and high speed of that motor
2nd thing, for some reason close of that motor they made 1 disconnecting switch for each speed instead of 1 with 6 wire to cut everything together. And if for some reason someone would leave the low speed disconnect switch off while the control is on high speed T1,T2,T3 will stay open which isnt good because in high speed on the diagram that say it should be all together.
What do you think ? Is it possible that one of these reason shorted that new motor again ?
So at my new job there is a motor that shorted twice that i cant confirm because the other electrician is gone.
And that motor is a 7.5hp 575v 2 speed star delta for a cooling tower.
I could blame the motor but i found 2 weird thing about the control of it
1st there is no timer or mecanical lock between the contactors used for the low and high speed of that motor
2nd thing, for some reason close of that motor they made 1 disconnecting switch for each speed instead of 1 with 6 wire to cut everything together. And if for some reason someone would leave the low speed disconnect switch off while the control is on high speed T1,T2,T3 will stay open which isnt good because in high speed on the diagram that say it should be all together.
What do you think ? Is it possible that one of these reason shorted that new motor again ?