What does the NEC Code say about hard-wiring a 220v electrical oven/range. I know many older houses are hard-wired and now the perferred method is a 4-wire/prong outlet. Is it still acceptable by code standards to hard-wire the range? Please provide NEC referrences. Thank you in advance for your insight.
 

·
Fried Bologna um um good!
Joined
·
8,094 Posts
The instructions with the range will tell you if it can be hard wired.

110.3 Examination, Identification, Installation, and Use
of Equipment.
(B) Installation and Use. Listed or labeled equipment
shall be installed and used in accordance with any instructions
included in the listing or labeling.
 

·
Registered
Joined
·
1,118 Posts
Some that I wires up, came with a pre- made whip... So yea hardwired!
 

·
NJ-IEC
Joined
·
14,387 Posts
Hard wire it (without cord and receptacle), but be sure to install a circuit breaker lockout device.

That's in 422 Appliances.
 

·
Registered
Joined
·
1,118 Posts
Magnettica said:
Hard wire it (without cord and receptacle), but be sure to install a circuit breaker lockout device.

That's in 422 Appliances.
Really? Do you know the reason for that? When did that start?
 

·
Fried Bologna um um good!
Joined
·
8,094 Posts
Hard wire it (without cord and receptacle), but be sure to install a circuit breaker lockout device.

That's in 422 Appliances.

If the manufacture say you can hard wire it then that is allowed. If the manufacture says cord you must use cord.
 

·
NJ-IEC
Joined
·
14,387 Posts
If the manufacture say you can hard wire it then that is allowed. If the manufacture says cord you must use cord.
You're right, and inspectors should enforce this instead of breaking balls on the peninsula receptacles! :laughing:
 

·
Banned
Joined
·
116 Posts
422

Hard wire it (without cord and receptacle), but be sure to install a circuit breaker lockout device.

That's in 422 Appliances.
That would suprise me if that's code for resi. I've never seen an inspector say or turn down anything hardwired resi before. Commercial of course

Waterheater, Oven, space heaters, etc...

Maybe I have a lazy inspector. I'll go check out 422 later
 

·
Administrator
Retired EC
Joined
·
23,167 Posts
Most cooktops and lay in Ranges used to be direct wired. I have done many that came with a whip of greenfield- FMC . You just install a jb behind the unit-- most ovens, single and double are this way also.
 

·
Banned
Joined
·
116 Posts
Hardwired

I've done 100's if not 1000's of hardwired resi home items and I've never had an inspector turn me down for no lockout on OCPD
 

·
Registered
Joined
·
931 Posts
if you dont have a lockout on a hard-wired appliance it is not code. many do not enforce, but the point is that a HO can energize it accidentally while the appliance guy has his hands in there.