1 - 1 of 1 Posts
Rest In Peace
2008 NEC
Clearances. Service-drop conductors shall not be readily accessible and shall comply with 230.24(A) through (D) for services not over 600 volts, nominal.
(A) Above Roofs. Conductors shall have a vertical clearance of not less than 2.5 m (8 ft) above the roof surface. The vertical clearance above the roof level shall be maintained for a distance of not less than 900 mm (3 ft) in all directions from the edge of the roof.
The above is what I have always went by when planing a service.
I have ran across situations that because of the above, I have had to relocate the service to comply.
After some reading I found Exception 2.
Exception No. 2: Where the voltage between conductors
does not exceed 300 and the roof has a slope of 100 mm in
300 mm (4 in. in 12 in.) or greater, a reduction in clearance
to 900 mm (3 ft) shall be permitted.
Has anyone ever used this exception and had the drop go across the roof?