Hi,

Are you allowed to double up wires on the 24 VDC Auxiliary Power in a Fire Alarm panel?

Will this pass verification?

Thanks!
1 - 6 of 6 Posts

· Registered
Power distribution and controls
Joined
·
2,926 Posts
Sorry I do not understand what your trying to convey.
Surely you know the rules about parallel conductors.
 

· Registered
Joined
·
9 Posts
Discussion Starter · #4 ·
It can be used for more than one device but there are limits. What are you trying to power with the AUX 24 volts?
There is an ice cube relay already powered by the FA panel for the 120VAC dampers and will need another source of 24VDC AUX PWR for the sounder base for the smoke devices.

My question is if you have to connect the aux power on the load side (via relay A1 & A2 coils) or can you directly wire in the aux power and have 2 wires in each terminal of the FA Panel to feed 2 different devices in parallel?

Thanks.
 

· Registered
Retired Low Voltage installer (Fire, Access, Security)
Joined
·
504 Posts
Not familiar with Canadian codes, but sounder bases are notification appliances and powered from the bell/horn/chime circuit in the panel (or bell booster). Wiring and supervision would follow the rules for any bell circuit. So no paralleling unless specifically allowed by the manufacturer.
 

· Light Bender
plumber
Joined
·
7,513 Posts
The manufacturer will specify if you can parallel off the aux 24 volts but my guess is no, you can’t.
More importantly, you will need to supervise the 24 volts For the sounder bases. Easy way to supervise the 24 volts is with an end of line relay.
 