Is it 120/240 Single phase or high leg delta? More information will help you here.How can one change an incoming 240V, 4wire to 120/208V WYE?
How difficult is that? I am assuming also expensive..Or get the POCO to change their transformers.
A high leg delta. The way it is wired...one of the phases is unused and the other two are feeding a single phase subpanel. We want to install a PV system. So we want to know whether there is a cost effective way of changing the voltage configuration without having to install 3 single phase inverters.Is it 120/240 Single phase or high leg delta? More information will help you here.
Check the listing of your 208 volt inverter. If it's good for 208 volts, it should be good for 240 volts -- since it's less overall current. And all the insulation ratings should be good for 250 volts anyway.A high leg delta. The way it is wired...one of the phases is unused and the other two are feeding a single phase subpanel. We want to install a PV system. So we want to know whether there is a cost effective way of changing the voltage configuration without having to install 3 single phase inverters.
Is it 120/240 Single phase or high leg delta? More information will help you here.
It is a small system. 13.08kW system and the inverter is:Check the listing of your 208 volt inverter. If it's good for 208 volts, it should be good for 240 volts -- since it's less overall current. And all the insulation ratings should be good for 250 volts anyway.
If not, then three 1-phase inverters will probably be cheaper than putting in a 208-240 volt, 3 phase transformer.
What's the kVA rating and manufacturer name of the inverter?
It is a small system. 13.08kW system and the inverter is:
http://www.svssolutions.com/wp-content/uploads/2012/08/SPR-10001f-1-UNI-SPR-11401f-1-UNI.pdf
Around here, the POCO will swap a delta bank for a wye at no cost. They're trying to get rid of deltas, especially pad-mount.How difficult is that? I am assuming also expensive..