Is it 120/240 Single phase or high leg delta? More information will help you here.
A high leg delta. The way it is wired...one of the phases is unused and the other two are feeding a single phase subpanel. We want to install a PV system. So we want to know whether there is a cost effective way of changing the voltage configuration without having to install 3 single phase inverters.
 

· Registered
Joined
·
654 Posts
A high leg delta. The way it is wired...one of the phases is unused and the other two are feeding a single phase subpanel. We want to install a PV system. So we want to know whether there is a cost effective way of changing the voltage configuration without having to install 3 single phase inverters.
Check the listing of your 208 volt inverter. If it's good for 208 volts, it should be good for 240 volts -- since it's less overall current. And all the insulation ratings should be good for 250 volts anyway.

If not, then three 1-phase inverters will probably be cheaper than putting in a 208-240 volt, 3 phase transformer.

What's the kVA rating and manufacturer name of the inverter?
 

· Registered
Joined
·
6 Posts
Discussion Starter · #11 ·
Is it 120/240 Single phase or high leg delta? More information will help you here.
Check the listing of your 208 volt inverter. If it's good for 208 volts, it should be good for 240 volts -- since it's less overall current. And all the insulation ratings should be good for 250 volts anyway.

If not, then three 1-phase inverters will probably be cheaper than putting in a 208-240 volt, 3 phase transformer.

What's the kVA rating and manufacturer name of the inverter?
It is a small system. 13.08kW system and the inverter is:
http://www.svssolutions.com/wp-content/uploads/2012/08/SPR-10001f-1-UNI-SPR-11401f-1-UNI.pdf
 

· Registered
Joined
·
654 Posts
Both of those links are getting flagged for me as malware. But if you can open and view them, it should be self-explanatory. Or, just call the manufacturer and ask to speak with one of their technical support people. I'm sure they will be able to answer your question.
 

· Bilge Rat
motors and controls.........
Joined
·
10,045 Posts
How difficult is that? I am assuming also expensive..
Around here, the POCO will swap a delta bank for a wye at no cost. They're trying to get rid of deltas, especially pad-mount.

If they're pole-mount and all 3 are the same size, they'll simply re-connect then internally and re-connect the service drop to a wye.
 