If your transformer is single phase side grounded (120 only) or delta delta you do not need secondary protection as long as the primary OCPD rating matches the secondary side per volt amp ratio.
In English terms if a secondary side protection device needs to be 100 amps at 240 volts you can omit it if the primary side OCPD is 50amps at 480 volts.