I'm looking at how to calculate a breaker for a three-phase circuit.

Given the following Full Load Currents (FLC):
  • Phase AB = 38 A continuous
  • Phase BC = 36 A continuous
  • Phase CA = 31 A continuous
I calculated the FLC for each phase to be:
  • A = 59.9 A
  • B = 64.1 A
  • C = 58.1 A
I'm wondering how three-phase breakers work. 64.1A x 1.25 = 80.125A. Does this mean a 85A breaker would be ideal for protecting this circuit as it covers our highest load (phase B)?

Thanks!
 

·
animal lover /rat bastard
Joined
·
13,547 Posts
is the 50 tripping ? or showing signs of overloading ?
 

·
Registered
Joined
·
1,437 Posts
This is my first time calculating a breaker for a three-phase source.

I have a fuse panel (we’ll call it FP #1) supplying another fuse panel (FP #2) with three phase power.
The output of FP #1 is fitted with a 50 A breaker. FP #2 is connected to 80 loads (unbalanced) which total the following:

Apparent Power: 12000 VA
Voltage: 120 V
Frequency: 60 Hz
Full Load Current (FLC):
  • Phase AB = 38 A continuous
  • Phase BC = 36 A continuous
  • Phase CA = 31 A continuous
I calculated the FLC for each phase to be:
  • A = 59.9 A
  • B = 64.1 A
  • C = 58.1 A
I feel like someone has put a 50 A breaker on FP #1 based on the maximum line-to-line current of FP #2 (38 A * 1.25 = 47.5). Am I correct in thinking that a three-phase breaker should be rated based on the average of the phase currents (59.9 + 64.1 + 58.1)/3 = 60.7A; 60.7A * 1.25 = 80 A breaker on a 80 A+ rated cable.

Thanks!
Your calcs need to be with 208 not 120. And your protecting the conductors feeding the other panel. So size at 1.25 percent of conductors. Screw the total load. Your ocpd cares about the conductor not what your putting on it.
 

·
Banned
Joined
·
7,230 Posts
This thread makes no sense. You can't be an electrician and not have any idea what you're talking about.

Edit: Oh wait, I remember you now! Okay, we can work this out.. but I think you're in over your head. lol
 

·
Registered
Joined
·
10 Posts
Discussion Starter #10
Give out the data (homework) you used to calculate this and we can show you how to do it right.
For phase A:
x=0.866*(AB + CA)
y=-0.5*AB + 0.5*CA
z=x + yj
|z|=(x+y) ^ 1/2
Current in Line 1 (Phase A) = 59.9A

This process is useful for unbalanced loads. For balanced loads I'd simply sum the currents, multiply by 3^1/2, and divide by 3. This value would then be used to find the circuit breaker rating (times FLC by 1.25 if continuous).

Hope this helps you understand what I'm trying to wrap my head around.
 

·
fertilizer distrubuter
Joined
·
1,250 Posts
For phase A:
x=0.866*(AB + CA)
y=-0.5*AB + 0.5*CA
z=x + yj
|z|=(x+y) ^ 1/2
Current in Line 1 (Phase A) = 59.9A

This process is useful for unbalanced loads. For balanced loads I'd simply sum the currents, multiply by 3^1/2, and divide by 3. This value would then be used to find the circuit breaker rating (times FLC by 1.25 if continuous).

Hope this helps you understand what I'm trying to wrap my head around.
And I thought I knew something. Now even apprentice calcs look like gibberish to me
 

·
fertilizer distrubuter
Joined
·
1,250 Posts
I have some time. I shall tell you how to calculate a 3 phase breakers current.

First disregarding nec:
look at the name plate flc on all 3 phase motors that current will be on all 3 legs.
Y208/120
Ex: 3phase 20a motor.

Ex: A 20a B 20a C 20a

Next add the flc for and loads across 2 poles that current will be on. AKA phase it is attached to.
Ex: Single phase 20 amp 208 volt motor. On phase a and b
Ex: 1000va heat strip on phases A and C. 1000/208=5a

Ex: A 45a B 40a C 25a

Last add any single phase loads attached to single phases.
Ex: 2400w microwave on phase C. 2400/120=20

Ex: A 45a B 40a C45a is the total current.

The nec states you must use 125% of the largest motor load (art 430) and any continuous loads.
Pro tip: When you are taking a test add another line to your line items label it 25% largest motor. That method makes it easier to check yourself and make changes.
 

·
Registered
Joined
·
12,167 Posts
I'm looking at how to calculate a breaker for a three-phase circuit.

Given the following Full Load Currents (FLC):
  • Phase AB = 38 A continuous
  • Phase BC = 36 A continuous
  • Phase CA = 31 A continuous
I calculated the FLC for each phase to be:
  • A = 59.9 A
  • B = 64.1 A
  • C = 58.1 A
I'm wondering how three-phase breakers work. 64.1A x 1.25 = 80.125A. Does this mean a 85A breaker would be ideal for protecting this circuit as it covers our highest load (phase B)?

Thanks!
I would round to the 80-amp breaker instead of the 85-amp breaker as far as the calculations go. If I was installing #4, I would use the 85-amp breaker.

Kind of a round about way of saying yes.
 