Hi all,

Can anyone assist please. We are currently renting 3 phase generators to provide a electrical supply to some A/C units, total running current per phase around 450-500 amps. As the generator comes bonded is their anyway I can ensure we have a sound earth when put on the ground. I have seen some generators with a Earth Spike..but some just on the ground. Due to ther running currents I want to be sure the earth is sound and the chiller will trip on a earth fault.?
Best regards

John
 

·
Registered
Joined
·
4,154 Posts
The Earth does not mean CRAP, the Earth could care less that you have a generator.


You need your electrician make sure the system GROUNDED CONDUCtOR/NEUTRAL/XO is bonded to the grounding electrode conductor in the facility. So all metallic components in your facility are at the same potential of the generator GROUNDED CONDUCtOR/NEUTRAL/XO.

BUT you also need to comply with all UK codes and standards.
 

·
Banned
Joined
·
11,766 Posts
The Earth does not mean CRAP, the Earth could care less that you have a generator.


You need your electrician make sure the system GROUNDED CONDUCtOR/NEUTRAL/XO is bonded to the grounding electrode conductor in the facility. So all metallic components in your facility are at the same potential of the generator GROUNDED CONDUCtOR/NEUTRAL/XO.

BUT you also need to comply with all UK codes and standards.


Not if the system is TT, which is allowed in BS7671. In that case earth is essential in clearing a fault on the chillers.
 

·
evil bastard
Joined
·
15,771 Posts
Not if the system is TT, which is allowed in BS7671. In that case earth is essential in clearing a fault on the chillers.
A tt system is very rarely used and essentially does not use an egc. Since we are required to use an egc, that didn't really apply. Even when a tt system is used the consumer is responsible to supply the grounding electrode system to earth.
 

·
Super Moderator
Licensed Electrical Contractor
Joined
·
11,748 Posts
Thanks for posting on ElectricianTalk.com. However, working with electricity and electrical systems can be unsafe if not done by a professional licensed electrician. The moderators of this site would like to advise you to contact a professional electrician in your area.

If you are permitted by law in your area to do your own electrical work, please sign up at our sister site, www.DIYChatroom.com where many of our professionals are also members and are looking forward to assist you with your needs.

Please take a moment to post your question at www.DIYChatroom.com If you're not already a member of DIYChatroom.com you can sign up for a free account by going to http://www.DIYChatroom.com/register.php/

We apologize for any inconvenience that this may have caused. This thread has been closed.
 
1 - 9 of 9 Posts
Status
Not open for further replies.
Top