just switched from resi to comm. and I worked for first time on a 3p 208Y panel today. Do you always run a ground with your "hot" from box to box or you can use the conduit as a ground path?
thanks
thanks
Added Security to run a ground . You do not have to run one , but after seeing
all the broken pipe runs in commercial work ceilings .
Pete
CEC permits EMT to be used at the EGC, however it is still a good idea to pull a wire. I was in an arena / college / high school the other day, and found that they were relying on the EMT as the EGC. Probably a huge cost savings on a job that size, but somehow a little unsettling.
Pool Shark
Here in the states there is a condition where medical healthcare facilities require a double redundant grounding system for certain areas. There is HCF MC cable that has a double redundant ground but I will run EMT with a secondary ground. It maybe more labor intensive but in certain jobs it is beneficial.
Are be talking about grounding or bonding?
if we are talking bonding (branch CCTs), I would have to say that in a steel structure building where conduit is strapped to steel perlings or gerts or Q deck or steel truss ect. like every 5 ft that the bonding is as good as you can get even if someone forgets to tighten a connector. so pulling a bonding conductor is a waste of money in that type of builing.