True.. but what I proposed is not a "listed" application... just a barnyard way of making it work.:laughing:Pete, what you described is a rotary phase converter (as opposed to a static converter that uses capacitors). Article 455 allows it.
If a 3Ø motor is connected to single phase power, it won't know what direction to turn, so it'll need its shaft turned a bit in order to get started. It'll also produce roughly 1/4 of its rated HP.Is it possible to connect a 3 phase motor to 240V single phase without a convertor? I'm not comfortable with motors as I used to be a construction electrician and just switched to commercial.
View attachment 34615
Please elaborate. This is a new one.You can also use another 3 phase motor to generate a third phase. In doing so you feed the generating motor single phase.
Pete
p.s. pretty sure it isn't code compliant but in a pinch it will work.
In this case, you're custom building a rotary phase converter.Please elaborate. This is a new one.
Personally, I think it's a poor excuse for a three phase source. IIRC, the motors sound sick, like they're single phasing. If you check the current draw on all three phases, you'll find a gross current imbalance.Yeah we call that a rotary phase converter.
![]()
I really don't like them. There a pain in the arse to troubleshoot.
Just for general info:... BUT your motor is realy a 1.25 HP due to the service factor rating. A 2HP drive is $271 or so.
I was told it was to compensate for the lack of different sizes. We had a air compressor that was 50 HP with a sf of 1.25 and the manufacture said it was because they did not make a 60 HP and that was what they needed. They said it would not hurt the motor and it ran for at least 20 yr that I know of.Y'know, it's sad, I work in a company that has a freaking motor rewind shop and I still can't get a clear explanation of service factor.
"A service factor of 1.25 allows you to run the motor at 125% of of the nameplate horsepower rating... but it damages the life expectancy by overheating the windings." Then what the hell is the point? I can run a 1.0SF motor at 125% and damage it just fine, too.
I've never seen an official explanation of how these companies are actually calculating SF.
The "official" wording in NEMA MG-1 is less vehement, it saysY'know, it's sad, I work in a company that has a freaking motor rewind shop and I still can't get a clear explanation of service factor.
"A service factor of 1.25 allows you to run the motor at 125% of of the nameplate horsepower rating... but it damages the life expectancy by overheating the windings." Then what the hell is the point? I can run a 1.0SF motor at 125% and damage it just fine, too.
I've never seen an official explanation of how these companies are actually calculating SF.
Alright, that's a good way of looking at it: It's a warrantied way of overloading the motor....But if the OEM wants to be cheap, he uses a 10HP with a 1.15SF. It will last out the warranty, that's all he cares about....
An SF rating is a requirement in NEMA MG-1 design specs if the motor is to be labeled as 'General Purpose'. But even though it is required, they go on to say "you shouldn't use it". It's weird, that's why the IEC people can't understand why we do it. But it has a lot to do with history. Long ago, the NEMA MG-1 description of SF used to mention "short time" overloads. But that was so nebulous that they either had to define it more specifically, or water it down to being generic by getting rid of all mention of time. They chose to water it down, probably because the specifics became way too complicated.Alright, that's a good way of looking at it: It's a warrantied way of overloading the motor.
So how are these guys determining the SF? I assume it doesn't follow the old Arrhenious rule-of-thumb where every 10° increase reduces service life by 50%. Like cowboy said, seems like some motors can run in SF indefinitely.
After I posted my reply, earlier today, I thought to myself, Why not just replace it with a dual voltage 1.5 HP 1760 single phase motor. It doesn't seem to be anything special, like a motor that is designed to be an integral part of a machine. They even make explosion proof, single phase motors.Thanks guys. Now I understand why the previous motor lasted only 2 years. It was installed by someone else and now I'm suppose to replace it. There was no OL or anything else, just a switch.
A lot of nameplates these days will state something like '1.0 SF using VFD power' or something to that effect when the normal SF is 1.15 or even higher.Just for general info:
Most motor mfrs will tell you that you cannot use the Service Factor of a motor AND run them from a VFD. One or the other, not both. Or put another way, all motors should be considered 1.0SF if run from a VFD.