Problem with wires burning up in peckerhead. Nothing is tripping out. When I fix the connections it goes back to running fine for a while. Wire size and over current protection is correct and all joints are good and secure. What would cause this, the motor?
 

·
Coffee drinking member
I pretwist and then use wire nuts. Solder pots rule.
Joined
·
13,959 Posts
Improper installation.
 

·
Coffee drinking member
I pretwist and then use wire nuts. Solder pots rule.
Joined
·
13,959 Posts
BBQ said:
What voltage? What size conductors? Have you taken a current reading? What is the ambient temp?
What frame, what type, were is it located, is it old or new, what work does it preform & are you an electrician or a carpenter?
 

·
Registered
Joined
·
89 Posts
Yes it would 'peak' at start up but that will not overheat the conductor due to the very short duration.
Gotcha. I was always told to be careful with that. Size a fuse too small without accounting for the motor start up amperage then it will burn up the fuse rather quickly.
 

·
Tool Fetish
Joined
·
944 Posts
If the FLA is 37, why are you running at 39? This would not cause the connection failure, but is there a mechanical load problem? What are your splices made with? We never make wire nut connections on any conductors over #10s.
 