Customer has dual 200 amp main panels with a 320 amp service. Bought a expensive 7500 watt ng generator for backup power. What’s the best way to feed this?

Right now thinking an indoor mounted 400 amp transfer switch and a 30 amp inlet on the outside. Price tag is coming out to $1,200. For his total price with generator and gas it makes sense to just get a small standby gen.
 

·
Super Moderator Beam Me Up Scotty
Elechicken
Joined
·
3,066 Posts
For a generator that small I'd do a small sub panel for the circuits he wants during an outtage. Maybe a 16 or 24 circuit panel. No way on a 7500 watt generator will you get to use everything from the 320 amp service...

Unless you meant to say 75 000 watt instead.

Sent from my SM-G920W8 using Tapatalk
 

·
Banned
Joined
·
39,205 Posts
Installing a 400 amp transfer switch should cost way more than $1200. The switch alone is extremely expensive and you have to rework the entire service.

But forget that idea altogether. You should just install an interlock on one of the 200 amp main panels. Backfeed a 30 amp breaker and run a 10-3 wire to an inlet.

Then just switch any circuits that he wants during an outage to the panel with the interlock.
 

·
Premium Member
Joined
·
18,747 Posts
Customer has dual 200 amp main panels with a 320 amp service. Bought a expensive 7500 watt ng generator for backup power. What’s the best way to feed this?

Right now thinking an indoor mounted 400 amp transfer switch and a 30 amp inlet on the outside. Price tag is coming out to $1,200. For his total price with generator and gas it makes sense to just get a small standby gen.
Ronk makes a very inexpensive double throw in both service rated and non-service rated:

https://www.ronkelectrical.com/meter-rite-grade-level-double-throw-switches-7416.php
 

·
Registered
Joined
·
1,543 Posts
I have a customer that wants to do the same thing, run a 320A/dual 200 service with a portable generator. Instead, I gave him a price on a standby 25KW natural gas generator with dual 200A, service entrance rated transfer switch. He hasn't decided yet.
The problem with a portable generator is, most are not rated for computer, electronics and circuit board use, and they're loud. The potable Honda EU7000iS is a good choice but costs almost $5,000. Another problem is gasoline storage.
For a $5,600, I can purchase both the 25KW and transfer switch.
 

·
Premium Member
Joined
·
18,747 Posts
Its my opinion that people have a little too much to drink and end up buying a generator for whatever reason.
They then sober up when they find out what they bought is wildly inappropriate for what need.
People somehow believe purchasing a generator is like buying a washing machine and think they can just call someone to install it.
 

·
Can't Remember
Joined
·
10,135 Posts
With the correct install and a customer who understands how manage loads, it could be ok, or a couple of selected circuit panels. Making people understand you need to run the portables regularly and use some fuel stabilizer seems to be one of the bigger challenges. I know he mentioned his was ng, but most aren't.
 

·
Can't sign em..forget em
Joined
·
7,439 Posts
Ronk makes a very inexpensive double throw in both service rated and non-service rated:

https://www.ronkelectrical.com/meter-rite-grade-level-double-throw-switches-7416.php
just for the sake of assuming... I assume the OP's service is fed in
parallel from the 320 amp meter socket enclosure to the 2 200
amp panels.

Does the Ronk product you posted , which is rated single phase @ 400
amps , have parallel lugs in it (or ate least able to accomodate them?)
 

·
Premium Member
Joined
·
18,747 Posts
just for the sake of assuming... I assume the OP's service is fed in
parallel from the 320 amp meter socket enclosure to the 2 200
amp panels.

Does the Ronk product you posted , which is rated single phase @ 400
amps , have parallel lugs in it (or ate least able to accomodate them?)
Yes it will take one big one or two smaller.
I have installed at least three of these from what I can remember. They are cheap, only a few hundred bucks and a decent size.
The major brand double throws are massive in size and at least 4x the price.
I purchase these through my electrical wholesaler as the price is about the same. Ronk, like most that sell to the public protects the electrical supply houses.
I didn't take very many pic of the 400 but have a few of a 200 we installed.
 

·
Premium Member
Joined
·
18,747 Posts
This is a pic of an installed


I cant deal with this sideways pic thing but.
We came out of a 320 meter, installed a 400amp main disconnect per the engineer. I could have used the SE model.
We then fed the utility side of the Ronk Switch. Out of there, we fed each of the existing 200 amp mains.
FWIW, this one was an open delta.

One more thing.
The utility side is connected to a set of 4/0 size camlocks at the bottom of the enclosure.
 

·
Premium Member
Joined
·
18,747 Posts
This one is a 200 amp.
Fed out of a meter-main combo. We fed the Ronk out of the feedthrough lugs.
the load side feeds a 200 amp main lug interior loadcenter.
This setup gives us a few circuits ahead of the generator for whatever might be needed outdoor such as a fixture indicating if utility power was restored, battery charger, heater, etc.

 

·
Registered
Joined
·
308 Posts
Put a mechanical interlock in each breaker panel, a wire out of each panel to a J-box, and a cord from there with a plug to plug into the generator
 

·
Registered
Joined
·
160 Posts
Discussion Starter #15
Put a mechanical interlock in each breaker panel, a wire out of each panel to a J-box, and a cord from there with a plug to plug into the generator


I think this is the most cost effective approach. Splitting the 30 amp inlet feed onto two 30 amp beakers with interlocks in each panel.
 

·
Banned
Joined
·
39,205 Posts
Put a mechanical interlock in each breaker panel, a wire out of each panel to a J-box, and a cord from there with a plug to plug into the generator
I think this is the most cost effective approach. Splitting the 30 amp inlet feed onto two 30 amp beakers with interlocks in each panel.
I don’t like that idea because if there is a bastard splice anywhere into the house you could backfeed into the grid when only switching one of the panels over.

Generally doing one panel should be enough for them, especially if you switch some circuits over to it.
 

·
Registered
Joined
·
160 Posts
Discussion Starter #17
I don’t like that idea because if there is a bastard splice anywhere into the house you could backfeed into the grid when only switching one of the panels over.



Generally doing one panel should be enough for them, especially if you switch some circuits over to it.


Trying to picture this in my head? Example? Been working all day maybe my brain is too fried.
 

·
Banned
Joined
·
39,205 Posts
Trying to picture this in my head? Example? Been working all day maybe my brain is too fried.
If you flip one interlock that will isolate that panel from the grid, but the other panel will still be connected to the grid and half of the circuits in the house.

I have found bastards splices in many houses in which two hots from completely different circuits were spliced together in a box. Nothing happened because they were on the same phase. But if this type of splice is in their house, when flipping only one interlock they could backfeed out into the grid. Or when the power returns it could feed through and destroy the generator.

It’s only 30A max, feeding a single 200A panel should get them what they need within the limits of the generator.
 

·
Super Moderator Beam Me Up Scotty
Elechicken
Joined
·
3,066 Posts
If you flip one interlock that will isolate that panel from the grid, but the other panel will still be connected to the grid and half of the circuits in the house.



I have found bastards splices in many houses in which two hots from completely different circuits were spliced together in a box. Nothing happened because they were on the same phase. But if this type of splice is in their house, when flipping only one interlock they could backfeed out into the grid. Or when the power returns it could feed through and destroy the generator.



It’s only 30A max, feeding a single 200A panel should get them what they need within the limits of the generator.
But with an interlock on only one panel this is still a possibility no?