400 Amp Meter Main 1969

403 6
Hi, please look at the two pictures. I think this is a 400 amp meter main. There are 4 Federal Pacific 100 amp disconnect switches in the garage, directly behind this meter main, which provides the disconnect for this equipment.
What is the yellow device in the middle of the picture? What is the u-shaped equipment that connects the left side line side to the load side bus? The right side of the equipment it appears the line side bus and load side bus are not connected. I think the #12 conductors tapped off of the bus is for the meter, which leads me to think this yellow device is some sort of current or voltage transformer, however it does not look like a transformer. Please help with determining how this equipment operates. Would removing the meter de-energize the load side? See pics. Thank you.

Attachments

1 - 2 of 2 Posts

· Registered
Power distribution and controls
Joined
·
2,871 Posts
The yellow thing is the CT for measuring one phase.

Incoming wire is mighty small for 400 amps.

Are you sure there is 240v inside? It does not look like the right side is continuous (?)

Pulling the meter has no effect on the power. Your looking at an old Meter CT cabinet.

No I have not see one exactly like this. Better verify the fault current before you go very far.
 