I have an existing 1 1/2 PVC pipe run to a barn, the homeowner wants a panel at the barn. Whats the largest size feeders that can be installed in the PVC? 120/240v single phase, 425ft long, 60 or 100amp is desired. HELP
Slave to the grind
It was answered in the other thread but, here it is again.
Using 56 amps of load, no more than 3% drop you would need 3/0 AL or #1 copper
Using 100 amps of load, no more than 3% drop you would need 350 AL or 4/0 copper.