1 - 11 of 11 Posts
· RIP 1959-2015
Is 517.19 D stating that the panelboard feeders for critical care areas are required to be a continuous metallic path back to the source?
Or is PVC acceptable?
No to PVC
517.19(D) Equipment Grounding and Bonding. Where a grounded electrical distribution system is used and metal feeder raceway or Type MC or MI cable that qualifies as an equipment grounding conductor in accordance with 250.118 is installed, grounding of enclosures and equipment, such as panelboards and switchboards, shall be ensured by one of the following bonding means at each termination or junction point of the metal raceway or Type MC or MI cable:
(1) 
A grounding bushing and a continuous copper bonding jumper, sized in accordance with 250.122, with the bonding jumper connected to the junction enclosure or the ground bus of the panel
(2) 
Connection of feeder raceways or Type MC or MI cable to threaded hubs or bosses on terminating enclosures
(3) 
Other approved devices such as bonding-type locknuts or bushings
250.118 Types of Equipment Grounding Conductors. The equipment grounding conductor run with or enclosing the circuit conductors shall be one or more or a combination of the following:
(1) 
A copper, aluminum, or copper-clad aluminum conductor. This conductor shall be solid or stranded; insulated, covered, or bare; and in the form of a wire or a busbar of any shape.
(2) 
Rigid metal conduit.
(3) 
Intermediate metal conduit.
(4) 
Electrical metallic tubing.
(5) 
Listed flexible metal conduit meeting all the following conditions:
a. 
The conduit is terminated in listed fittings.
b. 
The circuit conductors contained in the conduit are protected by overcurrent devices rated at 20 amperes or less.
c. 
The combined length of flexible metal conduit and flexible metallic tubing and liquidtight flexible metal conduit in the same ground-fault current path does not exceed 1.8 m (6 ft).
d. 
If used to connect equipment where flexibility is necessary to minimize the transmission of vibration from equipment or to provide flexibility for equipment that requires movement after installation, an equipment grounding conductor shall be installed.
(6) 
Listed liquidtight flexible metal conduit meeting all the following conditions:
a. 
b. 
For metric designators 12 through 16 (trade sizes 3⁄8 through 1 /2), the circuit conductors contained in the conduit are protected by overcurrent devices rated at 20 amperes or less.
c. 
For metric designators 21 through 35 (trade sizes ¾ through 1¼), the circuit conductors contained in the conduit are protected by overcurrent devices rated not more than 60 amperes and there is no flexible metal conduit, flexible metallic tubing, or liquidtight flexible metal conduit in trade sizes metric designators 12 through 16 (trade sizes 3⁄8 through ½) in the ground-fault current path.
d. 
e. 
(7) 
Flexible metallic tubing where the tubing is terminated in listed fittings and meeting the following conditions:
a. 
The circuit conductors contained in the tubing are protected by overcurrent devices rated at 20 amperes or less.
b. 
(8) 
Armor of Type AC cable as provided in 320.108.
(9) 
The copper sheath of mineral-insulated, metal-sheathed cable.
(10) 
Type MC cable that provides an effective ground-fault current path in accordance with one or more of the following:
a. 
It contains an insulated or uninsulated equipment grounding conductor in compliance with 250.118(1)
b. 
The combined metallic sheath and uninsulated equipment grounding/bonding conductor of interlocked metal tape–type MC cable that is listed and identified as an equipment grounding conductor
c. 
The metallic sheath or the combined metallic sheath and equipment grounding conductors of the smooth or corrugated tube-type MC cable that is listed and identified as an equipment grounding conductor
(11) 
Cable trays as permitted in 392.10 and 392.60.
(12) 
Cablebus framework as permitted in 370.3.
(13) 
Other listed electrically continuous metal raceways and listed auxiliary gutters.
(14) 
Surface metal raceways listed for grounding.
Informational Note:  For effective ground-fault current path, see 250.2 Definition.
Wouldn't rigid 90's with PVC qualify as meeting the above? I cannot find where panelboard feeders are required in a metallic pathway. 517.30C3 1-5 lists that pvc is an acceptable wiring method as long as it conforms
No PVC in a hospital.... NFPA-99
See post #2. PVC can be used for feeders, branch circuits serving patient care areas NO, it can not be used, see 517.13(A)
If PVC is used just pull the appropriate size EGC.
As Harry posted, if a metalic raceway is being used as the EGC it will have to be connected as described.
Edit, are we talking about the "Critical Branch" or just Critical Care areas including the Normal Branch?
I worked in patient care areas in hospitals for about 5 years and I can say I have never once seen PVC used for anything. Everything has to have redundant grounds (at least on the branch circuit side) so it was all metal conduit with a ground pulled in and bonded at each box with any splice in it.
I understand feeders are a different beast and all - and from reading the code section I don't see it specifically say no but I just have never seen it in any facility I have worked at. Not something i would want to fight with a state inspector or JCHAO.
JCAHO is only for their accreditation.... The AHJ is OSHPD
(12-years in hospitals)
1 - 11 of 11 Posts