GFCI is normally considered personnel protection and has a trip threshold of about 5 ma. GFP is considered equipment protection and has a higher threshold.
IMO, you would be making a mistake to install a 5 ma main protection device in a marina because of the nuisance tripping you mentioned.
Since you are installing a 3-phase service, I'm going to assume all of your receptacles for shore power will be no more than 30A. In that case, IMO you are better off using the exception and installing individual circuits to each slip (you could use a GFCI breaker). That way an offending boat will not cut off the whole marina and you will know where the offending boat is. Remember though, there are limits to the length of conductors for some GFCI breakers (I think 200 - 250' comes to mind).
IMO, you would be making a mistake to install a 5 ma main protection device in a marina because of the nuisance tripping you mentioned.
Since you are installing a 3-phase service, I'm going to assume all of your receptacles for shore power will be no more than 30A. In that case, IMO you are better off using the exception and installing individual circuits to each slip (you could use a GFCI breaker). That way an offending boat will not cut off the whole marina and you will know where the offending boat is. Remember though, there are limits to the length of conductors for some GFCI breakers (I think 200 - 250' comes to mind).