Discussion Starter · #1 ·
Hi All, I have a question maybe you guys can easily answer. I have purchased a Hubbell Electric Booster Heater for a commercial dishwasher. I am getting ready to run the branch circuit to supply power to the Water Heater. I pulled the following screenshot from the Owners Manual. The model that I have is the 240VAC 1PH 12KW highlighted below. I noticed that in the table they call for #6 wiring, 3/4" conduit and a 65A breaker. I have always thought that a branch circuit with #6 wire could be protected by a maximum of 60A breaker. Are their specs correct as far as NEC is concerned or should I go with #4 wiring for the 65A breaker?

Rectangle Font Line Parallel Pattern
 

· Registered
Joined
·
1,335 Posts
Fwiw, wire/cable temperature ratings and ampacities aren't universally the same across all jurisdictions. Also have to obey termination temperature ratings.

This concludes today's lesson of Electrical 101.
 

· Registered
Sub transient reactance X”d worshiper.
Joined
·
727 Posts
Fwiw, wire/cable temperature ratings and ampacities aren't universally the same across all jurisdictions. Also have to obey termination temperature ratings.

This concludes today's lesson of Electrical 101.
A question.

I am out of my element with acronyms.

What is Fwiw?
 

· Registered
Joined
·
3,596 Posts
#6 is good for 65a, 50a x 1.25 is 62.5, so it’s good. The 65a breaker is the same math.

You might be thinking 240.4(d), it applies to small conductors.
 

· Registered
Sub transient reactance X”d worshiper.
Joined
·
727 Posts
No to get too technical but I’m pretty sure FWIW is an initialism. “For what it’s worth”.

An acronym is an abbreviation that you can pronounce as a single word. Like Laser or potus for example.

😀
like NASA same as FWIW..... That is a acronym.

Thanks for the FWIW meaning.
 

· Registered
Electrical contractor 37 years. Electrical inspector 2 years
Joined
·
4,373 Posts
Is that chart correct? Is this just a heating element? A resistive heating element has a fixed resistance so if you lower the voltage the amperage will also be lower.
 

· Registered
Electrician/ Code Instructor
Joined
·
2 Posts
Hi All, I have a question maybe you guys can easily answer. I have purchased a Hubbell Electric Booster Heater for a commercial dishwasher. I am getting ready to run the branch circuit to supply power to the Water Heater. I pulled the following screenshot from the Owners Manual. The model that I have is the 240VAC 1PH 12KW highlighted below. I noticed that in the table they call for #6 wiring, 3/4" conduit and a 65A breaker. I have always thought that a branch circuit with #6 wire could be protected by a maximum of 60A breaker. Are their specs correct as far as NEC is concerned or should I go with #4 wiring for the 65A breaker?

View attachment 174537
65 amps is not a standard size breaker!
 

· Band Member
DIYer Extrodinaire
Joined
·
9,499 Posts
Both Eaton and Siemens make them.

Either way, MIN 65A breaker ... so what do you do ?? :p
 
  • Like
Reactions: Kevin

· Registered
Joined
·
2 Posts
Discussion Starter · #12 ·
Is that chart correct? Is this just a heating element? A resistive heating element has a fixed resistance so if you lower the voltage the amperage will also be lower.
That is correct EMTDOG. This is simply a water heater with a constant resistance heating element. There would be no startup load like a motor or compressor would have. Since the heater is 12KW and assuming the voltage is 240V the current would be right at 50A. The run is also relatively short as it is ~25 ft from the service panel. I just thought the #6 awg wiring was a little borderline for a 65A breaker. I suppose what some are saying here is that a constant draw of 50A is certainly OK for #6 wire and a 65A breaker will prevent any overheating or frying of the wire should an overload condition occur. Does that make sense?
 

· Registered
Electrical contractor 37 years. Electrical inspector 2 years
Joined
·
4,373 Posts
Look at the amps for 240 volts and then look at the amps for 208 vols. The amps for 208 volts is higher which makes me think the chart is not right. That is if I am reading it correctly.
 

· Chief Flunky
Field Service Engineer
Joined
·
4,174 Posts
Is that chart correct? Is this just a heating element? A resistive heating element has a fixed resistance so if you lower the voltage the amperage will also be lower.
At least NEC uses nominal (ANSI) voltages. Listing standards test at alternate conditions so as long as you follow that (such as +10%/-15% so normally you can ignore this.
 

· Administrator
Retired EC
Joined
·
24,975 Posts
Thanks for posting on ElectricianTalk.com. However, working with electricity and electrical systems can be unsafe if not done by a professional licensed electrician. The moderators of this site would like to advise you to contact a professional electrician in your area. If you are permitted by law in your area to do your own electrical work, please sign up at our sister site, www.DIYChatroom.com where many of our professionals are also members and are looking forward to assist you with your needs. Please take a moment to post your question at www.DIYChatroom.com If you're not already a member of DIYChatroom.com you can sign up for a free account by going to http://www.DIYChatroom.com/register.php/ We apologize for any inconvenience that this may have caused. This thread has been closed.
 