If the supply authority is providing my site with 600v wye would a 600v delta to 120/208 wye transformer still work?
I would just cap the neutral on the primary side.
 

·
Registered
Electrician
Joined
·
1,295 Posts
Transformer doesn't care if its Wye or Delta coming in on the primary. You will only have spots on the primary to hook up your 3 ungrounded conductors and EGC anyway.
 

·
Bilge Rat
motors and controls.........
Joined
·
7,369 Posts
Transformer doesn't care if its Wye or Delta coming in on the primary. You will only have spots on the primary to hook up your 3 ungrounded conductors and EGC anyway.
Also, there's no place to land the 347/600 neutral so do not run it.

As noted, a ∆ transformer is 3Ø 3 wire plus the ground. Nothing else.
 

·
Super Moderator Beam Me Up Scotty
Elechicken
Joined
·
3,066 Posts
If the supply authority is providing my site with 600v wye would a 600v delta to 120/208 wye transformer still work?
I would just cap the neutral on the primary side.