Discussion Starter · #1 ·
So, I have a work order to run a 480 3phase 60amp 4 wire circuit for some test equipment in a Raytheon Lab here in California. Midway through the job they inform me that they think it's a 30 amp not a 60 amp unit. They now are saying they me be wrong again and it is still 60amp.
ANYWAY, no biggie. this stuff happens. I just want to shoot out my plan and ask you guys for feedback as to weather or not it's a sound plan.
Simple, run 1". Pull #6's. (already did my voltage drop calc. I'm good.) install a 30 amp breaker at the panel, install a fusible 60amp disco at the unit and fuse it for 30. What do you guys think. That way, whatever happens I can make easy changes.
 