Already ordered extension rings.I highly doubt a 4 11/16 box is rated for 11 #8s, but I could be wrong. Might want to check your box fill on that one.
You only count one ground.Did the calcs on bbox fill the other day and I think I was short by the ground alone.
i just completed a job with 200 terminations just like that. one word: Blue WirenutsI have roughly 120 connections to make involving 4 #8's a piece. What's the best way to connect these. Only thing I can come up with is a insulated lug. Suggestions.
I guess to be clear I have 4 11/16 boxes with 3 flex whips and a 1" EMT entering it. TH e flex whips are comprised of 1 #8 black, whit, and green. From the 1" I have a mwbc with black red blue, white and green. The joints for the green will have 3# 8's and a #10. The neutral will have 4 #8's. Are insulated lugs or split bolts the only option to make these connections?
That's not one wordjrannis said:i just completed a job with 200 terminations just like that. one word: Blue Wirenuts
I know. I did the calc in my head the other and I think the box will hold all of the wires but when you insert the ground into the calc it is overfilled.You only count one ground.