2 1/8. I also have an mwbc passing through the box as well which increases fill.

WHips= 6 wires x 3=18
mwbc=4 wires x 3=12
mwbc pass through 4 wires=12
=42 cubic in which is legal in 4 11/16 until you add 2.5 cu in for the ground. Granted I think I only have this problem in 20 or 30 of my boxes (Doing a final count on Tuesday). But if I have to use insulated taps I may want extensions on all of them.
 

· Electrical Contractor
Joined
·
6,083 Posts
Too lazy to do a cross reference, but Bucannon 2011 will do 2#6 , should handle 3#8s .
Just have to find something for the 4 #8s
 

· Registered
Joined
·
1,623 Posts
Some brand of preinsulated "Polaris" type connector will be the fastest/cheapest way to do this. These connectors will take up a lot of box space and with the number of conductors, a larger box would save some aggravation.
 

· Registered
Joined
·
12,135 Posts