The building next to the 18 unit we are getting ready to start has a 120/240 single phase 800 amp main breaker, feeding (18) 125 amp mains and one 200 amp house meter. the contractor ran three set of 250 aluminum to the transformer. Does this sound correct???
 

· Registered
Joined
·
2,655 Posts
The building next to the 18 unit we are getting ready to start has a 120/240 single phase 800 amp main breaker, feeding (18) 125 amp mains and one 200 amp house meter. the contractor ran three set of 250 aluminum to the transformer. Does this sound correct???
That's probably what the utility specified which is usually smaller gauge than the NEC. Local power company here will run one set of 250al for a 400 amp service.
 

· Registered
Joined
·
809 Posts
MTW said:
That's probably one of the single most ignorant comments I've ever read on these forums.
Is it really. We ran what our poco told us to for a 600 amp service following what they told us we needed. Our inspector red tagged it and we had to redo 80' of ug feeders then our inspector told us that they have the final say not the poco
 

· Banned
Joined
·
16,850 Posts
Is it really. We ran what our poco told us to for a 600 amp service following what they told us we needed. Our inspector red tagged it and we had to redo 80' of ug feeders then our inspector told us that they have the final say not the poco
If the poco assumes ownership of the lateral (some poco's do, some don't), then the inspector has no jurisdiction over it.
 

· Registered
Joined
·
809 Posts
MTW said:
If the poco assumes ownership of the lateral (some poco's do, some don't), then the inspector has no jurisdiction over it.
Thats what happened was poco told me everything more than once then the inspector tagged it and after that poco said nope were not gonna be responsible. Our chief inspector said not to rely on what they say just because of that.
 

· Registered
Joined
·
809 Posts
sparky402 said:
Thats what happened was poco told me everything more than once then the inspector tagged it and after that poco said nope were not gonna be responsible. Our chief inspector said not to rely on what they say just because of that.
Yea i was working with the head guy in that area and he wrote it all up and then when it came time to do it that guy got called to the service and the new guy said yea thats what we gotta do but then they all backtracked
 

· Registered
Joined
·
10 Posts
Thats what happened was poco told me everything more than once then the inspector tagged it and after that poco said nope were not gonna be responsible. Our chief inspector said not to rely on what they say just because of that.
Must be a regional thing. Here poco just hooks and unhooks power. From their connections on down the inspector has the say on the matter which usually conforms to the NEC.
 