Unfortunately im no gas guy... Lp co is coming to check, as i didnt connect gas... Is this hard to check gas? What tools needed?nrp3 said:Gas pressure would have to be measured to see whether it's out of the 10-12 inches of water column. This connector problem can be intermittent.
You should check the water columns to see if they are within operating pressureI tried starting 4 times after resetting alarm. It would run for like 3 seconds and then show same alarm.... I saw about hi gas psi online and had owner turn on all other gas appliances, and it started... Tried it Repeatedly and worked every time! I simulated loss and ran and xfered like it should.
Wtf?
allen wrench and a manometerUnfortunately im no gas guy... Lp co is coming to check, as i didnt connect gas... Is this hard to check gas? What tools needed?
Forgot to look at the $500.00 manual. It defaults fuel pressure issues to RPM sensing. Test 50 ,check water columns .I agree, but sure enough that code directs you to tests 50 and 64. Fuel and coil ground wire.
suppose to be an updated manual coming out in the springNot $500 but not cheap either. I don't do electronic copies. Like my paper based texts. Sometimes the tests lead you down the garden path and you miss the more obvious mechanical issues like a head gasket. Or maybe not so obvious. Been and still a new learned skill.
It's too cold!!!!Installed it 6 months ago and owner noticed not exercising. Any ideas?
1. There is a separate gas reg, 5' from gen. Ad its lp...
View attachment 33431