So I have a service Im changing out on saturday. I need to cut the service drop and when finished I was gonna use an insulated burndy to temp it before com ed gets there. However, it snowed today and am a lil nervous to mess with the service drop standing on the snow due to moisture. Any thoughts and helpful input?
 

· Premium Member
Joined
·
20,221 Posts
So I have a service Im changing out on saturday. I need to cut the service drop and when finished I was gonna use an insulated burndy to temp it before com ed gets there. However, it snowed today and am a lil nervous to mess with the service drop standing on the snow due to moisture. Any thoughts and helpful input?
No one here is going to tell you to do it but, do you possess at least some 00 gloves and some basic PPE?
 

· :-)
Joined
·
3,664 Posts
Standing on the snow?

You know of course not to complete the circuit.

Fibreglass ladder comes to mind to start with. Keep the body off the earth... and anything that can attach your body to the earth such as the service conduit and the bare neutral from the power companies service drop.

Like a bird.

As for ppe, some will wear a space suit. Some, if done as above, will find an old pair of leather gloves and others won't bother and just do it.

Be careful. Keep your elbow off the service conduit. Wait or perhaps pay overtime to have the power company do it.
 

· Registered
Joined
·
132 Posts
Discussion Starter · #8 ·
daveEM said:
Standing on the snow? You know of course not to complete the circuit. Fibreglass ladder comes to mind to start with. Keep the body off the earth... and anything that can attach your body to the earth such as the service conduit and the bare neutral from the power companies service drop. Like a bird. As for ppe, some will wear a space suit. Some, if done as above, will find an old pair of leather gloves and others won't bother and just do it. Be careful. Keep your elbow off the service conduit. Wait or perhaps pay overtime to have the power company do it.
Yes i have one of those electrician ladders. Im thinking of thowing some towels underneath it to lessen the moisture.
 

· Moderator
Estwing magic
Joined
·
28,218 Posts
Yea it will no prob. So would placing dry blankets under it provide add. Protection
Those dry blankets will soak up moisture like a sponge.

Personally, I'm a real wuss when it comes to this kind of work. I would delay the job until the power company could give it to me cold or not do it at all. This kind of sh!t scares me and I fully admit it.
 

· Registered
Joined
·
132 Posts
Discussion Starter · #16 ·
99cents said:
Those dry blankets will soak up moisture like a sponge. Personally, I'm a real wuss when it comes to this kind of work. I would delay the job until the power company could give it to me cold or not do it at all. This kind of sh!t scares me and I fully admit it.
Yes me too. I always get it in my head that it will arc out even if im not in the path.
 

· Moderator
Estwing magic
Joined
·
28,218 Posts
Here it's common practice to have the utility guy come out in the morning to do the disconnect. He gives me his shoe phone number and I phone him when I'm close to job completion. He then comes back to do the reconnect.

Maybe this can work for you too, Staples?
 

· Registered
Joined
·
132 Posts
Discussion Starter · #18 ·
99cents said:
Here it's common practice to have the utility guy come out in the morning to do the disconnect. He gives me his shoe phone number and I phone him when I'm close to job completion. He then comes back to do the reconnect. Maybe this can work for you too, Staples?
It takes 5-10 days for com ed to come out and 1-3 days to reconnect. Customer cant do that with temps in the negatives
 

· Registered
Joined
·
11,599 Posts
Just do it. I would not stand on the top rung but I would do this in a second. No need to put anything under the ladder if it is fiberglass. It is not the ground moisture that is gonna get you. Its touching the neutral.
 

· Registered
Joined
·
132 Posts
Discussion Starter · #20 ·
sbrn33 said:
Just do it. I would not stand on the top rung but I would do this in a second. No need to put anything under the ladder if it is fiberglass. It is not the ground moisture that is gonna get you. Its touching the neutral.
Yes, thanks. This is what im using. Ill just tape the heck out my a ratchet for this.



 