ALL thermal overload protective devices, as those are, are REQUIRED to take time to reset. The time is carefully chosen by virtue of the bi-metal strip materials in an attempt to approximate the thermal cool-down constant of the motor, meaning the rate at which the motor will cool down based on standard design conditions.
The difference between A-B and Tele in that respect would be that Tele, being a French company, bases their design on IEC motors, which have NO service factor and require fast tripping OLs set at class 10 or lower. That means the motors tripped a lot sooner, therefore they are not as hot and cool off faster. A-B on the other hand, being a North American company, bases the reset time on NEMA motor designs, which allow for a 1.15 service factor and a class 20 trip. So yes, the AB versions will take longer to reset, but that's because it held in a lot longer and the motor got a lot hotter. The Tele versions will trip more often if using a NEMA motor, or to look at it the other way, the Tele will not allow you to take advantage of the added thermal capacity of a NEMA motor.
The AB units are OK with "zero stacking" meaning mounting right next to each other. But ALL bi-metal OL devices are susceptible to high ambient heat inside the box. The trip times are based on the device being in a 25C environment, and have automatic compensation to adjust themselves for up to 40C (104F). But after that, all bets are off. Each unit gives off about 9 watts of heat, so if you have dozens of them in a box, it all adds up. So if you are POSITIVE that the motors are not really being overloaded, then it's likely a cumulative heat problem in your enclosure.