yes 30 amp would be fine
what article in the NEC are you referring to by "80% of breaker" ?Hey guys quick question, I have a ac unit says min. Amp 26, max breaker 45. Would I be ok with a 30 amp circuit or no because I'll be over 80% of my 30 amp breaker?
Yep. You'll find it in the Urban Legend Electrical Code.Thanks guys I just thought that it was rule of thumb not to load up a breaker more than 80%. Thanks again.
Really?yeah. the 80% rule usually applies for branch circuits
like bedrooms , bathrooms ect... lighting and power. the AC , is dedicated
being that you are a 4th yr apprentice (according to your profile), if you are planning on taking your test and/or the contractor/master test, it would be a great idea to study the articles that apply so you know where to look for the answers to the questions that you have been asking. It is no small task to prepare for the test, and while it is perfectly ok to ask these questions, it is vital to you becoming an independant tradesman that you be able to find this stuff when you need it, and directly from the book. start at 240 and see how it leads to 440 for this item, and it will help you out.Thanks guys I just thought that it was rule of thumb not to load up a breaker more than 80%. Thanks again.
what types of problems?.. and yes obviously 10awgSince nobody mentioned I will.
Put a 10 wire to that and a 40 amp breaker. If you put a 30 on it you may get problems years down the road.
As the unit gets older, or if the voltage happens to be a little low the minimum size breaker may be more prone to tripping.what types of problems?.. and yes obviously 10awg
I always use the max not the minimumSince nobody mentioned I will.
Put a 10 wire to that and a 40 amp breaker. If you put a 30 on it you may get problems years down the road.
^^^This. A 45 amp breaker is only a couple more dollars and may prevent getting called out on the hottest day of the year because someone's AC keeps trippingI always use the max not the minimum
So what? Only continuous loads are limited to 80%.yes, bedroom circuits have variable loads