Adjustable amperage for EVSE - Ontario new bulletin

482 Views 9 Replies 4 Participants Last post by  Navyguy
Yesterday ESA released their new bulletins.

Previously we could only wire an EVSE to a lower setting if it was configured using internal dip switches but now, Bulletin 86-1-5 allows wiring an EVSE to a lower amperage setting when it can be set using commissioning amps and software.

The bulletin also allows the use of EVSE that can load share to be on one circuit
Product Rectangle Font Parallel Diagram
See less See more
  • Like
  • Helpful
Reactions: 2
1 - 3 of 10 Posts
That is correct, but lets not confuse that with the user app. If it can be adjusted by a "user app" then it needs to wired to max rating. The commissioning software is usually "authorized" persons only such a a factory rep, service technician, etc. So basically the same as the previous "dip switch" rule, just now they have included factory software used by authorized personnel.

Cheers
John
  • Like
Reactions: 1
I don't know, but that was the issue previously. A user could "crank up" the output via an app... or at least that is what I understood the issue to be. I don't have an EVC, so I don't specifically know.

Cheers
John
I think this only really applies to "hard wired" units, because if they "plug in" we are still back to the receptacle / wire / breaker matching requirement. So unless the unit has a 15-30P or a 6-30P, I think you are still going to have to use the 15-50R or 6-50R installation.

Cheers
John
  • Like
Reactions: 1