AFCI Receptacle as Good as an AFCI Breaker

11706 Views 62 Replies 22 Participants Last post by  don_resqcapt19
This guy doesn't think so. I wonder why? Maybe because Eaton doesn't make the receptacles!:whistling2:

  • Like
Reactions: HARRY304E
1 - 20 of 63 Posts

· Retired Account
Joined
·
39,616 Posts
Yet another manufacturing mouthpiece yammering on about the protective qualities of an afci, while failing to inform us of how they specifically work to do so.....:rolleyes: this really is getting to be our trades global warming issue .


~CS~
 

· Registered
Joined
·
3,830 Posts
If the AFCI really works and if ~40% of the faults that they are expected to catch are in the fixed building wiring (from the original proposals to require AFCIs), then the receptacle AFCI removes protection from a section of the fixed building wiring, so he would be correct.
 

· felonious smile.
Joined
·
15,896 Posts
I would feel perfectly safe with a 1972 Slater receptacle feeding a space heater on old #14 TW wire circuit protected by a FPE breaker. As long as the side screw terminals are used.
 
  • Like
Reactions: TOOL_5150

· felonious smile.
Joined
·
15,896 Posts
On a serious note, I roughed in a small sunroom addition from a local circuit. Now I'm having a hardtime finding this infertile device in any local supplyhouse. No one stocks them yet around here.
 

· THE "BIG RED MACHINE"
Joined
·
3,413 Posts
If the AFCI really works and if ~40% of the faults that they are expected to catch are in the fixed building wiring (from the original proposals to require AFCIs), then the receptacle AFCI removes protection from a section of the fixed building wiring, so he would be correct.
So is the receptacle arc fault method miss out in protecting the home run and maybe breaker panel?
 

· THE "BIG RED MACHINE"
Joined
·
3,413 Posts
In theory the receptacle AFCI can provide series arc fault protection between the source and the device. It cannot provide parallel arc fault protection between the source and the device.
so where do you locate the device in relationship to the daisy chain? ( first receptacle in line, last one in line, anywhere in the circuit?)
 