Okay, I listened to a podcast that someone post on the forum today. Very informative. Thank you. One item they mentioned was Afci protection for kitchens in a dwelling unit.

Would this be correct for 2014 code compliance with Afci circuits?

All lighting circuits
Dishwasher
Disposal
Small appliance branch circuits
Microwave (120 volt)

Am I missing anything else?
 

·
Administrator
Retired EC
Joined
·
23,572 Posts
Here is the art. Laundry room is included

210.12 Arc-Fault Circuit-Interrupter Protection. Arcfault
circuit-interrupter protection shall be provided as required
in 210.12(A) (B), and (C). The arc-fault circuit interrupter
shall be installed in a readily accessible location.
(A) Dwelling Units. All 120-volt, single-phase, 15- and
20-ampere branch circuits supplying outlets or devices installed
in dwelling unit kitchens, family rooms, dining
rooms, living rooms, parlors, libraries, dens, bedrooms,
sunrooms, recreation rooms, closets, hallways, laundry areas,
or similar rooms or area
s shall be protected by any of
the means described in 210.12(A)(1) through (6):
(1) A listed combination-type arc-fault circuit interrupter,
installed to provide protection of the entire branch circuit
(2) A listed branch/feeder-type AFCI installed at the origin
of the branch-circuit in combination with a listed outlet
branch-circuit type arc-fault circuit interrupter installed
at the first outlet box on the branch circuit. The first
outlet box in the branch circuit shall be marked to indicate
that it is the first outlet of the circuit.
(3) A listed supplemental arc protection circuit breaker installed
at the origin of the branch circuit in combination
with a listed outlet branch-circuit type arc-fault circuit
interrupter installed at the first outlet box on the branch
circuit where all of the following conditions are met:
a. The branch-circuit wiring shall be continuous from
the branch-circuit overcurrent device to the outlet
branch-circuit arc-fault circuit interrupter.
b. The maximum length of the branch-circuit wiring
from the branch-circuit overcurrent device to the
first outlet shall not exceed 15.2 m (50 ft) for a
14 AWG conductor or 21.3 m (70 ft) for a 12 AWG
conductor.
c. The first outlet box in the branch circuit shall be
marked to indicate that it is the first outlet of the
circuit.
(4) A listed outlet branch-circuit type arc-fault circuit interrupter
installed at the first outlet on the branch circuit
in combination with a listed branch-circuit overcurrent
protective device where all of the following
conditions are met:
a. The branch-circuit wiring shall be continuous from
the branch-circuit overcurrent device to the outlet
branch-circuit arc-fault circuit interrupter.
b. The maximum length of the branch-circuit wiring
from the branch-circuit overcurrent device to the
first outlet shall not exceed 15.2 m (50 ft) for a
14 AWG conductor or 21.3 m (70 ft) for a 12 AWG
conductor.
c. The first outlet box in the branch circuit shall be
marked to indicate that it is the first outlet of the
circuit.
d. The combination of the branch-circuit overcurrent
device and outlet branch-circuit AFCI shall be identified
as meeting the requirements for a system
combination–type AFCI and shall be listed as such.
(5) If RMC, IMC, EMT, Type MC, or steel-armored Type
AC cables meeting the requirements of 250.118, metal
wireways, metal auxiliary gutters, and metal outlet and
junction boxes are installed for the portion of the
branch circuit between the branch-circuit overcurrent
device and the first outlet, it shall be permitted to install
a listed outlet branch-circuit type AFCI at the first outlet
to provide protection for the remaining portion of
the branch circuit.
(6) Where a listed metal or nonmetallic conduit or tubing
or Type MC cable is encased in not less than 50 mm
(2 in.) of concrete for the portion of the branch circuit
between the branch-circuit overcurrent device and the
first outlet, it shall be permitted to install a listed outlet
branch-circuit type AFCI at the first outlet to provide
protection for the remaining portion of the branch
circuit.
Exception: Where an individual branch circuit to a fire
alarm system installed in accordance with 760.41(B) or
760.121(B) is installed in RMC, IMC, EMT, or steelsheathed
cable, Type AC or Type MC, meeting the requirements
of 250.118, with metal outlet and junction boxes,
AFCI protection shall be permitted to be omitted.
 

·
Banned
Joined
·
15,674 Posts
Discussion Starter · #4 ·
Thanks Dennis. I need to open up the new code book and study up on the new requirements. Do you have the 2014 NEC on an iPad or as a PDF?
 

·
Administrator
Retired EC
Joined
·
23,572 Posts
I bought the Book with a pdf download. I don't have an Ipad just my pc
 

·
Banned
I make all the electrons line up for their Flu shots
Joined
·
33,456 Posts
I am going to be submitting a proposal for the next NESC that requires arc fault protection for all electrical circuits at the source of the circuit. Should be a reasonable fix for all the problems everywhere.
 

·
Retired Account
Joined
·
39,697 Posts
Europe's isn't afci- is it? I thought it was gfci or as they call it RCD

Europe has an advanced system in comparison to the American one Denny, mainly due to their having to rebuild and rethink it after WW2

I started a thread on it quite a while back, our foreign devil brethren were kind enough to chime in

It is, imho, worthy of consideration given our (since the 02?) international nec status

~CS~
 

·
Retired Account
Joined
·
39,697 Posts
RCD, it has a higher trip level and is not trouble free as Steve is trying to make it sound.

Marc could talk about this.
they have RCD's in descending order main, sub main, breaker. Think split buss on steriods

iirc, the 30ma is on par with our afci's 30ma , which is about all an afci does anyways

~CS~
 

·
Retired Account
Joined
·
39,697 Posts
Again,
my point of total house afci protection stands, if CMP-2 thinks they're that great you'd think they'd be ALL OVER IT

they just want to sell us 30 of them instead of 1

when some of you EC's are confronted with 30 in a 40 for a fat decade , you'll eventually come to the same conclusion, if not be confronted by your customers realizing what they're paying for

~CS~
 

·
Administrator
Retired EC
Joined
·
23,572 Posts
they have RCD's in descending order main, sub main, breaker. Think split buss on steriods

iirc, the 30ma is on par with our afci's 30ma , which is about all an afci does anyways

~CS~
Yes our afci have a different ma trip then an afci but an afci is more than that. IMO, an AFCI in a main would be a nightmare
 

·
Banned
I make all the electrons line up for their Flu shots
Joined
·
33,456 Posts