Are you sharing a neutral on the AFCI circuit? I don't think single-pole AFCIs can share a neutral.
That would be also be my question. Is anything else causing it to trip?My only other suggestion is: Is it just the drywallers screwgun that is causing it to trip? If so, there's a problem with the screwgun.
Try another drill and see if it trips.My only other suggestion is: Is it just the drywallers screwgun that is causing it to trip? If so, there's a problem with the screwgun.
If this was the case it wouldn't matter if it was the drywaller's screw gun or not, the circuit would trip on ANY load..
The only explanation I can think of is that the screw on the tomic connector has scored both the 14/2 and the 12/2 and is creating a short across the 2 circuits.
If this was the case the AF breaker would never hold.The wrong neutral was landed on the arch falt breaker.
Agreed.If this was the case it wouldn't matter if it was the drywaller's screw gun or not, the circuit would trip on ANY load.
Disagree. No load, this would hold, but ANY load would trip itIf this was the case the AF breaker would never hold.
Agreed. This is usually what ends up being done, If the problem isn't neutrals mixed up at the panel. (sigh....)Somewhere along the line the circuits running together. I'd start from around a mid point in one of the circuits and just start pulling things apart. Sometimes you've gotta go through the whole dang thing until the problem is revealed.
Wow, I never heard that. I've been using them for years, especially when fishing into an existing panel. What I like about using them in a new panel is that they are fast and they really keep all the wires bundled together in one place. That keeps the work really neat and clean. None of my inspectors has ever said anything about it -in fact, during the rough insp, I got complimented on how good the panel looked (my generally well-trained and hard working helper did it all).The odd thing about this is you still use tomic conn. They have been illegal for like 20 years.
I am 64 years old, forgot too much. Help. I got customer wants 50ampere RV receptacle installed. RV is not on site. I assumed 2 hots, neutral and grounding. Four wire receptacle. His dealer tells me make sure 2 hots are same leg so no potential for 240 is present. So now dowe use 1 hot jumpered to other prong, and neutral and grounding. I don't know too much about RV stuff, inspector said he don't either. Please advise. Any info appreciated.
Your question is a good one, how ever you should start a new post with it so as not to confuse this one.
The codes for RV and parks have changed greatly, unless you have access to the new code book I would respectfully recomend some one else tackle this.:thumbsup: