In researching a paper I am putting together for revamping maintenance practices I came across the following worth the read.
http://www.aluminum.org/sites/default/files/Aluminum%20Building%20Wire%20Installation%20%26%20Terminations.pdf
http://www.aluminum.org/resources/electrical-faqs-and-handbooks/electrical
In Particular
FAQs and Answers For Aluminum Alloy Building Wire
Q1) What are the relative conductivities of aluminum and copper?
Aluminum has 61% the conductivity of copper on a volume basis and 200% the conductivity of copper on a weight basis.
- See more at: http://www.aluminum.org/resources/electrical-faqs-and-handbooks/electrical#sthash.rbQYkAju.dpuf
Q3) Why is copper used more often for smaller wire sizes?
Copper, having been available to mankind for thousands of years, was readily available at the beginning of the electrical industry in 1882. At that time, aluminum was only available in very small quantities, so it was a precious metal more valuable than gold or silver. Ninety-five percent of all the aluminum ever produced was made after WWII; and by then, the electrical industry had developed using copper. Over the past few decades, aluminum has increasingly replaced copper for electrical applications. The transformation started on the utility grid thru transmission, distribution, and has continued down to service drop, service entrance and building wire feeders.
In the United States today, copper is typically the only choice available for branch circuit wiring. Receptacles and switches are usually rated only for copper, and are less expensive than CO/ALR devices. - See more at: http://www.aluminum.org/resources/electrical-faqs-and-handbooks/electrical#sthash.rbQYkAju.dpuf
Q4) Is there a certain kind of aluminum that must be used for building wire?
Yes. In most cases, you must use an AA-8000 series aluminum alloy building wire as required in NEC 310.14. There are some exceptions, notably underground service entrance conductors that terminate outside a building. - See more at: http://www.aluminum.org/resources/electrical-faqs-and-handbooks/electrical#sthash.rbQYkAju.dpuf
Q9) Is joint compound required to be used on aluminum to prevent corrosion?
Only if the connector manufacturer or local codes specifically require it. The NEC does not require oxide inhibitor for either aluminum or copper, but it does require that you follow manufacturers’ installation instructions for listed products.
However, even if oxide inhibitor is not specifically required, it is recommended for both aluminum and copper conductors to prevent ingress of moisture and the possibility of subsequent corrosion. Both copper and aluminum conductors will corrode if installed in corrosive environments. Proper installation and choice of connector help to prevent corrosion at connections.
Oxide inhibitors are also tested for specific uses. Be sure to follow manufacturers recommendations and use only inhibitors specifically listed for the conductor type and voltage class you are installing.
Q10) Do aluminum connections need to be periodically tightened to maintain a good electrical connection?
No. Connections on either aluminum or copper should not be retightened after installation following manufacturers’ installation instructions. Connector test performance requirements are based upon no retightening. NFPA 70B, Recommended Practice for Electrical Equipment Maintenance, does not call for retightening aluminum conductors. Connections should only be tightened if there is evidence of a loose connection. Both over-tightening and under-tightening can cause failure of aluminum or copper connections. Unwarranted re-tightening of screw-type connectors can lead to failure of the connection with either aluminum or copper conductors - See more at: http://www.aluminum.org/resources/electrical-faqs-and-handbooks/electrical#sthash.rbQYkAju.dpuf
In Particular