I want to run #1 Al ser cable (4 conductor) to feed a 100 amp sub panel, in a residential setting .Since it is not NM I assume I can use table
310.15(B)(16) 75 degree column which allows me to put this sub feed on a 100 amp breaker.Is my reasoning right? What code reference directs me to SER cable.Article 338.10 (4) tells me to use the 60 degree column if installed in thermal insulation.I am running this thru a crawl space and up some interior walls with no insulation around the wire.Does this sound like a compliant installation?
310.15(B)(16) 75 degree column which allows me to put this sub feed on a 100 amp breaker.Is my reasoning right? What code reference directs me to SER cable.Article 338.10 (4) tells me to use the 60 degree column if installed in thermal insulation.I am running this thru a crawl space and up some interior walls with no insulation around the wire.Does this sound like a compliant installation?