Really the risk is just overloading a neutral conductor.
Lets just say the normal circuit gets loaded to 75%.. but then you've stolen that neutral to be the return for another circuit.. and you're loading that circuit to 75%.. that neutral could have 150% of it's rated power going through it.
That equates to heat, the insulation could over heat and break down and you could lose the neutral. Losing a neutral can be a really bad thing, destroying equipment.
If someone's going to pull the hot (switch leg) through the EMT, just pull it's neutral along for the ride.