I have a situation where there is a detached garage that is powered from a residence, and then the power continues from that detached garage to another completely separate utility shop, (or garage), after that. - Is there a problem with this? I am thinking no. If I am correct, I just have to make sure each garage has no more than one circuit, (multiwire is okay), and that each garage has a disconnect, (a snap switch disconnect will do.)
I guess I just question powering multiple buildings from the same circuit. I hope this makes sense. Thanks in advance. P.S. power consumption and loads are not my consideration here. They just want basic lights and convenience plugs.
 

·
Registered
Joined
·
2,325 Posts
Sounds good, as long as the branch circuit has an equipment ground, and each building has a lighting outlet, a convenience GFCI outlet, and disconnecting means.
 