Amperage of the units?.Thanks but let's try for a more reasonable solution. The problem in question involves banks of heaters, where one heater craps out from time to time, taking the contactor with it.
You are a wise man99cents said:I assume that a contactor closing into a fault will become extinct very quickly.
Heaters crap out from time to time. No way to forecast. Just getting expensive replacing relays all the time99cents said:Why is the heater crapping out? Fuse it.
I've looked at solid state relays and in answer to your question I've already up sized relays two sizes. The ovens have staged heating so the relays are opening and closing 100 times per cycle. 3 cycles a day. I meg out these heaters as a matter of course every few months (to cut out bad ones) but there's no way to know.Big John said:Fused solid state relays can have wicked high short-circuit current ratings. Many manufacturers publish coordination info that show what combination of fuses are needed to get to a specific SCCR. You can get well up to 100kA with this method, but you'll still be paying to replace fuses. Out of curiosity, what kind of contactors are you using? Upsizing a NEMA contactor would get you a lot more life than an exactly sized IEC contactor. Why are these failing this frequently? You might consider putting some sort of ground-fault protection on them, and maybe you'd catch an impending failure before it turned into a hard short.
Why can't you fuse individual heaters? I'm not trying to be a d!ck here, just asking questions.Can't fuse individual heaters. Banks are currently fused as previously mentioned
Think about a motor starter, they close iwith inrush current every time it closes,I assume that a contactor closing into a fault will become extinct very quickly.
Well, we still don't know where you started from, so saying that you upsized twice is meaningless. You also don't describe your circuit very well, ie is this single phase, 3 phase? Hopefully it is 3 phase, because 9kW @ 480V would be 18.75A, and you said it was a 15A breaker. So if it is an even 3 phase distribution to the elements, then 10.83A per phase, what size contactor were you using? If you started with a 10A relay and went to 12A then 15A, that will not hold up to anything but running current, not fault capability at all. But if you started with 20A, then went 40A, then 90 A, that's a different story.I've looked at solid state relays and in answer to your question I've already up sized relays two sizes. The ovens have staged heating so the relays are opening and closing 100 times per cycle. 3 cycles a day. I meg out these heaters as a matter of course every few months (to cut out bad ones) but there's no way to know.