The inspector just wrote us up saying that the laundry washer needs to be an arc fault breaker, is that code ?
 

·
Moderator
Estwing magic
Joined
·
26,372 Posts
Dunno if it's code but if a vacuum cleaner trips an AFCI breaker then a washing machine certainly can.
 

·
Registered
Joined
·
712 Posts
NEC 2014 states:

210.12 Arc-Fault Circuit-Interrupter Protection. Arcfault circuit-interrupter protection shall be provided as required in 210.12(A) (B), and (C). The arc-fault circuit interrupter shall be installed in a readily accessible location.
(A) Dwelling Units. All 120-volt, single-phase, 15- and 20-ampere branch circuits supplying outlets or devices installed in dwelling unit kitchens, family rooms, dining rooms, living rooms, parlors, libraries, dens, bedrooms, sunrooms, recreation rooms, closets, hallways, laundry areas,
or similar rooms or areas shall be protected by any of the means described in 210.12(A)(1) through (6).
 

·
Moderator
Estwing magic
Joined
·
26,372 Posts
NEC 2014 states:

210.12 Arc-Fault Circuit-Interrupter Protection. Arcfault circuit-interrupter protection shall be provided as required in 210.12(A) (B), and (C). The arc-fault circuit interrupter shall be installed in a readily accessible location.
(A) Dwelling Units. All 120-volt, single-phase, 15- and 20-ampere branch circuits supplying outlets or devices installed in dwelling unit kitchens, family rooms, dining rooms, living rooms, parlors, libraries, dens, bedrooms, sunrooms, recreation rooms, closets, hallways, laundry areas,
or similar rooms or areas shall be protected by any of the means described in 210.12(A)(1) through (6).
It takes a lot of hookers to get a rule like that one passed.
 

·
Moderator
Estwing magic
Joined
·
26,372 Posts
If you look at the guys making all the arc fault proposal they work for major companies. Guys on the CMP are even affiliated with them.


Is it any better in Canada?
It is for now because we only have to AFCI protect bedroom receptacles. But Canada has hookers too :( .
 

·
Registered
Joined
·
374 Posts
Every city is different. Besides that I'm working for industrial contractor and I have an employee doing the residential stuff
Cities might have some local regulations but the whole state is under the 2013 California Electrical Code which is based on 2011 NEC and your inspector needs to read upon it. Definitely no AFCI requirement for laundry circuit. 210.12(A) Rip him a new one...
 

·
Premium Member
Joined
·
7,413 Posts
Discussion Starter · #16 ·
Cities might have some local regulations but the whole state is under the 2013 California Electrical Code which is based on 2011 NEC and your inspector needs to read upon it. Definitely no AFCI requirement for laundry circuit. 210.12(A) Rip him a new one...
Thanks, This city has a few of there own local codes :( but the problem is that I am working in a plant starting at 6:00 am, and have no time !! My employee is frazzled, and the multi unit apartment owner is pushing as typical :laughing:
 

·
Administrator
Retired EC
Joined
·
23,666 Posts
What room is the washer in? If it is in a bedroom then yes it needs afci but if it is in a laundry room then No it does not however not all inspectors see it that way.
 

·
Registered
Joined
·
1,099 Posts
Thanks, This city has a few of there own local codes :( but the problem is that I am working in a plant starting at 6:00 am, and have no time !! My employee is frazzled, and the multi unit apartment owner is pushing as typical :laughing:
Then you lost this one. Install the AFCI and move on!
 

·
Premium Member
Joined
·
7,413 Posts
Discussion Starter · #19 ·
What room is the washer in? If it is in a bedroom then yes it needs afci but if it is in a laundry room then No it does not however not all inspectors see it that way.
Hall closet converted into a new laundry room. Plumbing already signed off.
Times 2 apartments, and eventually more.
 