I have seen product pictures of grounding bushings that can be added on after conductors were pulled into conduits. I have no idea if such animals exist any longer it was a fair long time ago .
Hi all,
I just want to find out when circuits of over 250 volts to ground DONT need ground busing connectors. I know Article 250.97 gives the following exceptions
(a) Threadless couplings and connectors for cables withmetal sheaths
(b) Two locknuts, on rigid metal conduit or intermediate metal conduit, one inside and one outside of boxes and cabinets
(c) Fittings with shoulders that seat firmly against the box or cabinet, such as electrical metallic tubing connectors,
flexible metal conduit connectors, and cable connectors, with one locknut on the inside of boxes and cabinets
(d) Listed fittings that are identified for the purpose
A job i'm on came with a factory installed 277/480v service panel feeding a factory installed 480v VFD. The 480V HAS a ground bushing at the service feeders but none of the loads coming out of it do. its my understanding is that 480v EMT or sealtite load circuits coming out of the panel would require a ground bushing. Any input much appreciated.
See pics below one is from 480 feeder panel other is where it lands at VFD