Water treatment plant in the same town as the police station with the UPS and buck boost set up from my other thread is having an issue with their transfer switch.
It happens very seldom, but they called me out to see if I could determine anything.
It's an ASCO switch, 230 amp 480 volt 3 phase, pretty straightforward simple unit with a minimal interface. They do a weekly exercise test on it, where they will run the generator and actually switch the plant over to it for 30 minutes or so. It is supposed to time out on its own and switch back to normal utility power after the exercise period is over. Most of the time it works great, but 2 or 3 times in the past it has stayed on and never switched back to utility power.
According to the plant operator, once he realized, "Hey the generator sure has been running for a while," he went down and looked at the switch and sure enough, the indicator light for "Utility Power Available" was lit up as expected, but for some reason the transfer switch did not transfer back.
The other issue happened just a week or two ago. They ran the generator's exercise like normal but when the exercise period was up, the transfer switch switched back to utility power but all the lights and equipment shut off. Turned out the breaker feeding the utility supply to the transfer switch had tripped right at switchover.
It's not a GFP breaker or anything; just a standard molded case breaker. I did a FOP test on it and measured around 20-35 mV dropped across each breaker pole at approximately 75 - 100 amps per leg. Pretty darn good, I'd say. I don't dare meg the feeder and branch circuits though, it's supplying toooooooooooons of instruments, drives, etc. I can't imagine why that breaker would trip right at switch over. Haven't been able to duplicate it for a recording meter either.
Any thoughts?
It happens very seldom, but they called me out to see if I could determine anything.
It's an ASCO switch, 230 amp 480 volt 3 phase, pretty straightforward simple unit with a minimal interface. They do a weekly exercise test on it, where they will run the generator and actually switch the plant over to it for 30 minutes or so. It is supposed to time out on its own and switch back to normal utility power after the exercise period is over. Most of the time it works great, but 2 or 3 times in the past it has stayed on and never switched back to utility power.
According to the plant operator, once he realized, "Hey the generator sure has been running for a while," he went down and looked at the switch and sure enough, the indicator light for "Utility Power Available" was lit up as expected, but for some reason the transfer switch did not transfer back.
The other issue happened just a week or two ago. They ran the generator's exercise like normal but when the exercise period was up, the transfer switch switched back to utility power but all the lights and equipment shut off. Turned out the breaker feeding the utility supply to the transfer switch had tripped right at switchover.
It's not a GFP breaker or anything; just a standard molded case breaker. I did a FOP test on it and measured around 20-35 mV dropped across each breaker pole at approximately 75 - 100 amps per leg. Pretty darn good, I'd say. I don't dare meg the feeder and branch circuits though, it's supplying toooooooooooons of instruments, drives, etc. I can't imagine why that breaker would trip right at switch over. Haven't been able to duplicate it for a recording meter either.
Any thoughts?