I have been researching for awhile now and need some general feedback on the topic. The question is for a air handler in the attic, can a form of disconnect means be a plug in outlet or does it need a fuse/non fuse able disconnecting means. Home inspector said it can't be a outlet per NEC CODE. Any help is greatly appreciated. And code reference is a huge help.
 

·
Administrator
Retired EC
Joined
·
23,672 Posts
I have been researching for awhile now and need some general feedback on the topic. The question is for a air handler in the attic, can a form of disconnect means be a plug in outlet or does it need a fuse/non fuse able disconnecting means. Home inspector said it can't be a outlet per NEC CODE. Any help is greatly appreciated. And code reference is a huge help.
IMO unless the furnace is equipped with a factory cord then it must be direct wired. It can be just a snap switch for a gas furnace or a non fused a/c type disconnect would work for 240v units
 

·
Registered
Joined
·
1,576 Posts
Dennis Alwon said:
IMO unless the furnace is equipped with a factory cord then it must be direct wired. It can be just a snap switch for a gas furnace or a non fused a/c type disconnect would work for 240v units
I thought cord and plug could be used for a means of disconnect regardless if it's field wired.
 

·
Administrator
Retired EC
Joined
·
23,672 Posts
I thought cord and plug could be used for a means of disconnect regardless if it's field wired.
I believe you will find the manufacturer instruction will not allow it
 

·
Registered
Joined
·
109 Posts
Discussion Starter · #6 ·
I appreciate the quick feedback. Anymore code references. It might be me but if feel like home inspectors need a refresher on code rather than what they feel it should be.
 

·
Administrator
Retired EC
Joined
·
23,672 Posts
The only code reference would be 422.16. If you look at the list and the qualification in(A) I think you will see that the inspector has a good argument besides the 100.3 (B) mentioned by Ken-- he had a typo and had (C)
 

·
Administrator
Retired EC
Joined
·
23,672 Posts
422.16 Flexible Cords.
(A) General. Flexible cord shall be permitted (1) for the
connection of appliances to facilitate their frequent interchange
or to prevent the transmission of noise or vibration or
(2) to facilitate the removal or disconnection of appliances that
are fastened in place, where the fastening means and mechanical
connections are specifically designed to permit ready removal
for maintenance or repair and the appliance is intended
or identified for flexible cord connection.
(B) Specific Appliances.
(1) Electrically Operated In-Sink Waste Disposers. Electrically
operated in-sink waste disposers shall be permitted
to be cord-and plug-connected with a flexible cord identified
as suitable in the installation instructions of the
appliance manufacturer where all of the following conditions
are met:
(1) The flexible cord shall be terminated with a groundingtype
attachment plug.
Exception: A listed in-sink waste disposer distinctly marked
to identify it as protected by a system of double insulation, or
its equivalent, shall not be required to be terminated with a
grounding-type attachment plug.
(2) The length of the cord shall not be less than 450 mm
(18 in.) and not over 900 mm (36 in.).
(3) Receptacles shall be located to avoid physical damage
to the flexible cord.
(4) The receptacle shall be accessible.
(2) Built-in Dishwashers and Trash Compactors. Built-in
dishwashers and trash compactors shall be permitted to be
cord-and-plug-connected with a flexible cord identified as
suitable for the purpose in the installation instructions of
the appliance manufacturer where all of the following conditions
are met:
(1) The flexible cord shall be terminated with a groundingtype
attachment plug.
Exception: A listed dishwasher or trash compactor distinctly
marked to identify it as protected by a system of
double insulation, or its equivalent, shall not be required to
be terminated with a grounding-type attachment plug.
(2) The length of the cord shall be 0.9 m to 1.2 m (3 ft to
4 ft) measured from the face of the attachment plug to
the plane of the rear of the appliance.
(3) Receptacles shall be located to avoid physical damage
to the flexible cord.
(4) The receptacle shall be located in the space occupied
by the appliance or adjacent thereto.
(5) The receptacle shall be accessible.
(3) Wall-Mounted Ovens and Counter-Mounted Cooking
Units. Wall-mounted ovens and counter-mounted cooking
units complete with provisions for mounting and for
making electrical connections shall be permitted to be permanently
connected or, only for ease in servicing or for
installation, cord-and-plug-connected.
A separable connector or a plug and receptacle combination
in the supply line to an oven or cooking unit shall be
approved for the temperature of the space in which it is
located.
(4) Range Hoods. Range hoods shall be permitted to be
cord-and-plug-connected with a flexible cord identified as
suitable for use on range hoods in the installation instructions
of the appliance manufacturer, where all of the following
conditions are met:
(1) The flexible cord is terminated with a grounding-type
attachment plug.
Exception: A listed range hood distinctly marked to identify
it as protected by a system of double insulation, or its
equivalent, shall not be required to be terminated with a
grounding-type attachment plug.
(2) The length of the cord is not less than 450 mm (18 in.)
and not over 900 mm (36 in.).
(3) Receptacles are located to avoid physical damage to the
flexible cord.
(4) The receptacle is accessible.
(5) The receptacle is supplied by an individual branch
circuit.
 